Mounting inverter outside

I'm thinking of putting a Samlex PST3000 inverter outside under a deck canopy. It'll be protected from rain and overnight moisture and wind...until we get another hurricane. 10 miles from the ocean so salt air is a minor concern.
At first I rejected the idea but then space and convenience took hold. Then I thought about people that put them on sailboats and trawlers where inverters exist in a humid salt air environment constantly.
This is a tropical location so...
Thoughts?
At first I rejected the idea but then space and convenience took hold. Then I thought about people that put them on sailboats and trawlers where inverters exist in a humid salt air environment constantly.
This is a tropical location so...
Thoughts?
8- 235Watt panels, 2 strings in series/parallel, 4L16 Deka 6Volt, 370AH FLA. batteries, 3000W Cotek pure sine inverter, SRNE ML2440 40Amp Controller & 40 Amp Renogy controller, 24 Volt system.
4 stand alone PV arrays; 12V gate opener, 24V Dankoff rain water pumping system, 12V Shurflo rain water garden pumping, 12V bathroom LED lighting and fan.
2- 450 Watt Phonosolar panels with 4 L16 6 volt batts./ Renogy Tracer 40 Amp controller/ Samlex 3000W Inverter.
2- 450 Watt Phonosolar panels with 4 L16 6 volt batts./ Renogy Tracer 40 Amp controller/ Samlex 3000W Inverter.
Honda EU3000W generator for backup.
Comments
I like the battery and power center thing I mae from similar to a design I saw in Homepower or a Backwoods Solar article.
Current setup at new place, battery is a forklift battery that started life in the battery box above and moved to new home! It's in a 'skin tight' box to the right of the power center;
- Assorted other systems, pieces and to many panels in the closet to not do more projects.
Inverters need to run cool (and, ideally, at a stable temperature). But they do not need "air exchange"--especially if that air is moist/has salt in it... A "small" inverter in a large(r) box with good internal air circulation (don't put "hot inverter" at top of box, under self, etc.) will usually be OK... Keep box in shade/cool helps.
Electronics in general, age 2x faster (1/2 the aging life) for every 10C(18F) over room temperature (25C/77F)... Run inverter at 95F, it will last 1/2 as long (on average).
Temperature cycling is also a killer for electronics... Freezing in AM, >100F in afternoon sun--That can cause solder joints and component failures too.
-Bill
No need to be concerned about cold temps. Overnight lows might get to mid 60's...I read that these Samlexes are Taiwan production so better than typical Chinese mfr. (think I read it here) so I'll probably put it outside on the concrete wall.
My main concern was with humidity but inside the house it would only be marginally lower.
2- 450 Watt Phonosolar panels with 4 L16 6 volt batts./ Renogy Tracer 40 Amp controller/ Samlex 3000W Inverter.
The house is cinder block/concrete and drilling holes is easy enough but can I run all these wires through one hole rather than two? I'd use a length of pvc pipe thru the wall probably to house them in, either 3/4" or 1" diameter.
It's just easier to drill one hole!
2- 450 Watt Phonosolar panels with 4 L16 6 volt batts./ Renogy Tracer 40 Amp controller/ Samlex 3000W Inverter.
In general, you want the charge controller to be at the same temperature as the battery bank (i.e., don't want controller at 70F, and the batteries at 0F to 100F. The charge controller should be setup to adjust charging voltage for battery bank based on "battery" temperature (typically around -5mV per degree C per Cell).
If the charger has a "remote battery temperature sensor"--Then mounting the charger inside is not an issue.
Second question... There are several issues with using the same "conduit" for DC and AC wiring...
In the NEC, the wiring for the "low voltage circuit" needs to have the same insulation voltage rating as the shared lines in the "high voltage" circuit (120/240 VAC wiring is 600 VAC minimum insulation rating--Therefore the 12/24/48 VDC wiring needs the same minimum insulation rating.
Also NEC does not support running low voltage wiring (i.e., 12 VDC "touch safe") in the same conduit as 120+ VAC wiring.
When you get into ROMEX--I am not sure if running two ROMEX in the same hole is the same as wiring sharing the same conduit (probably not?).
Since this is not an NEC installation--As long as you are "safe" (right insulation for right voltages)--Not an issue.
Next. Bringing solar panel wiring into the home. If you have lightning strike possibilities--You want to be very careful here.
I would not overlook mounting the charge controller on the outside wall (in a ventilated box to avoid weather/sun) and keep that all separate (panel wiring away from wiring going into the home. This may suggest getting a remote LCD display for the charge controller (if available) so you can monitor your system inside the home.
Also, for lightning, you can get a nice set of DC and AC surge suppressors, with 6 AWG ground wire to an 8-10 foot ground rod outside the building (next/near foundation--keep ground wiring short and straight/gentle bends).
https://www.solar-electric.com/search/?q=surge+protection
Lastly--Many times there is a lot of "hash" on DC power lines (and even from solar panel power lines). To keep radio/RF noise to a minimum, avoid parallel runs of AC+DC wiring next to each (bundle tied together, in same conduit run, etc.). Generally, cross DC and AC wiring at right angles to avoid too much coupling of noise.
Or in this case, if sharing same hole in wall--Separate AC and DC wiring as soon as the wiring leaves the "hole" (both outside and inside of wall).
-Bill
The main reason I wanted the controller inside was to be able to check voltage easier but since it's under the awning it's only a mattter of going outside the kitchen door to check. Here in this climate the door is always open when we're home anyway. Unless we get a hurricane.
So the only wires going through the wall now will be 2 Romex AC wires to the inside outlets.
I'll look into the surge protection link, thanks. We get frequent lightning strikes in summer but so far we haven't lost anything, although many friends have stories to tell.
Now humidity is another story. Picture South Florida type.
2- 450 Watt Phonosolar panels with 4 L16 6 volt batts./ Renogy Tracer 40 Amp controller/ Samlex 3000W Inverter.