wire gauge?
trying to figure out what gauge of wire to use running from a bank of 4 s460's to a 3524 panel...any suggestions are appreciated...shane
Re: wire gauge?trying to figure out what gauge of wire to use running from a bank of 4 s460's to a 3524 panel...any suggestions are appreciated...shane
Use the voltage drop calculator listed in this post:
http://forum.solar-electric.com/showthread.php?t=29
http://www.uwgb.edu/nevermab/voltage_drop_calculator_.xlsPowerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
Re: wire gauge?
Here’s my take on this question using the 2005 US National Electrical Code:
(1) NEC 690.8(A)(4): maximum inverter current = ((3500 VA / 85% efficiency) / 21 VDC min) = 196 A.
(2) NEC 690.8(B)(1): Conductors and overcurrent protection devices must be rated for 125% of maximum current, so 196 A x 125% = 245 A.
(3) Recommended DC input breaker is 250 A, which is next standard size up from 245 A; looks OK to me.
(4) Wire ampacity based on conditions of use (inverter max power spec based on 25 C ambient):(a) 90 C wire corrected for 25 C ambient and two conductors run in conduit between battery box and breaker panel: Ampacity requirement = 250 A / 1.05 = 238 A; 4/0 AWG wire (260 A) meets requirement per NEC 310.16.(b) 90 C wire corrected for 25 C ambient, derated for 75 C breaker terminal spec and “free air” (not in conduit) connection to breaker: Ampacity requirement = 250 A / 1.05 = 238 A; 2/0 AWG wire (265 A) meets requirement per NEC 310.17.Worst case condition of use is (a), so 4/0 wire is required. Looks like this is in agreement with recommendations from OutBack forum.
HTH,
Jim / crewzer
- 234 Forum & Website