Does stacking inverters increase DC input current capacity?
johnhall6095
Registered Users Posts: 27 ✭✭
Hey guys. Sorry if this is a stupid question but I've poured over my inverter docs and googled/read for a few hours and can't seem to find a straight-forward answer on this question. I have two SE XW6048 inverters (stacked in parallel). The docs rate a single XW6048's input current capacity at 130 amps. Does stacking the two inverters increase the maximum DC input current capacity to 260 amps?
15kW PV, Grid-tie + 1210AH Deka lead acid battery bank, 2 x XW6048, 2 x MTTP60-150, 1 x MTTP100-600, SCP, Gateway
If you have one battery bank--Yes, the two inverters' DC input current(s) add and draw that from the battery bank.
In the end, the total AC loads on the inverters needs to be supported by DC input current and voltage... For example (using generic values):- 10,000 Watts AC load * 1/0.90 inverter eff * 1/52 volts DC battery bus = 213.7 Amps @ DC bus
Thanks Bill. Yes, I have one battery bank.15kW PV, Grid-tie + 1210AH Deka lead acid battery bank, 2 x XW6048, 2 x MTTP60-150, 1 x MTTP100-600, SCP, Gateway
are you talking about using the inverter as a Charger for the batteries ?
No, just wanted positive confirmation that inverter stacking (parallel) increases total inverter DC input current capacity. Thanks again guys!15kW PV, Grid-tie + 1210AH Deka lead acid battery bank, 2 x XW6048, 2 x MTTP60-150, 1 x MTTP100-600, SCP, Gateway
