Outback psx-240 standby power use
Estragon
Registered Users Posts: 4,498 ✭✭✭✭✭
Does anyone know what the standby or idle power use is on an Outback psx-240 autotransformer? I'll be using for a submersible pump, and am trying to figure out if it needs to be somewhere handy to turn it on and off. Also, does the fan run much and if so, is it noisy?
I think they claim a dozen watts loss or so, it's one of the better/efficient transformers. The fan cycle rate will depend on the size of the pump, small pump, no fan, large pump, more run time. The noise it makes, I don't know about.Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
My PSX-240 runs 10-12 watts according to the Kill-A-Watt meter. About 28 - 30 watts with only the heat pump on it turned off.12K asst panels charging through Midnite Classic 150's, powering Exeltechs and Outback VFX-3648 inverter at 12 and 48 volts. 2080 AH @ 48 VDC of Panasonic Stationary batteries (2 strings of 1040 AH each) purchased for slightly over scrap, installed August 2013. Outback PSX-240X for 220 volt duties. No genny usage since 2014.
Okay, thanks. 10-12 watts isn't bad at all. It'll only be on during the day anyway, as we switch from 7 kw 48v system to low watt 12v system at night.Off-grid.
Thanks for these comments, even if dated. This prompts consideration and the possibility for a load actuated contactor on the 110 AC input to control on/off.
If you are going to be switching that transformer on and off frequently, note that it presents a hefty load to the inverter each time the magnetic core charges up. Repeat enough and it could be hard on a small inverter. Something like a pre-charge or soft start might be worth looking.
I have a Trace Engineering T240 3.9kva rated auto transformer that consumes 14 watt hours. Not an Outback but similiar.
I had a T240 running a 240vac submersible well pump. Xantrex 4048 inverter. When the pump would cycle and turn on the auto trans at the same time the colour would dissapear and the picture shrink inwards from the edges of the tv set (CRTube type). I once saw the Xantrex status meter hit 45 amps ac when this happened (as high as it would read). The tv eventually died and I replaced the water pump with a Grundfos soft starter. Much easier on equipment not having that incredible surge on startup.
I still use the autotransformer(s) for running my mini split heatpumps,, but in an always on mode when heating or cooling. -
mike95490 said:If you are going to be switching that transformer on and off frequently, note that it presents a hefty load to the inverter each time the magnetic core charges up. Repeat enough and it could be hard on a small inverter. Something like a pre-charge or soft start might be worth looking.
Split phase inverters have a imbalance factor. XW's I think can handle 75% No idea about other brandsPowerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
- 228 Forum & Website
- 618 Discussion Forums/Café
