Looking for help understanding maximum charging current...
Asinnobooks
Registered Users Posts: 3 ✭
Hello all!
On the brink of setting up my first solar system as part of my van conversion.
Looking at:
400W / 24V Panel
2 x 200Ah / 12V Gel Batteries
And am trying to work out what MPPT solar charge controller is required. The batteries say they have a maximum charging current of 37.5A, which I imagine i want to get as close to as possible in order to charge the battery as quickly as possible, but looking at descriptions of charge controllers it seems that they are rated more based on the amperage input (which i think would be 8A in my case - 400W/24V...). I also see recommendations for a 40A CC for 400W panel, but do i run the risk of damaging or destroying the battery as this amperage is great than the batteries' max. charging curren?
I'm a bit lost and hope you may be able to help me get my head round all this.
Many thanks
On the brink of setting up my first solar system as part of my van conversion.
Looking at:
400W / 24V Panel
2 x 200Ah / 12V Gel Batteries
And am trying to work out what MPPT solar charge controller is required. The batteries say they have a maximum charging current of 37.5A, which I imagine i want to get as close to as possible in order to charge the battery as quickly as possible, but looking at descriptions of charge controllers it seems that they are rated more based on the amperage input (which i think would be 8A in my case - 400W/24V...). I also see recommendations for a 40A CC for 400W panel, but do i run the risk of damaging or destroying the battery as this amperage is great than the batteries' max. charging curren?
I'm a bit lost and hope you may be able to help me get my head round all this.
Many thanks
Tagged:
Comments
-
Welcome to the forum Asinnobooks,
GEL batteries are (many brands/models) are not great for solar power systems... They are great for sitting unused and during discharge. However during charging, many (some, many, most?) have issues with high charging current/higher charging voltages).
GEL batteries have "gelled" type electrolyte (basically sulfuric acid+water+silica gel)--the downside being at high charging currents/voltage the GEL battery can gas which forms gas bubbles in the electrolyte--And this can permanently cause a loss in capacity of the GEL battery.
AGM batteries (absorbed glass mat) batteries are very similar to GEL batteries, without the problem of forming gas bubbles in the GEL electrolyte.
Always start with the settings in the Battery Specifications--But the numbers are roughly (12 volt bank, 24 bolt bank is 2x higher):- 14.75 volts set point for Flooded Cell batteries
- 14.40 volts set point for AGM
- 14.20 volts set point for AGM
Charging current wise--For "longest" life, around 10% to 13% rate of charge for Lead Acid type batteries is recommended. And if your controller has the option, use a remote temperature sensor to monitor battery bank temperature (higher temperature lead acid battery, lower charging voltage required).. For 13%+ rate of charge, highly recommend a RBTS (remote battery temperature sensor) to ensure a happy and healthy battery (and for RVs that run from deserts to snow country, RBTS are really helpful).
For GEL batteries--Many recommend a 5% rate of charge (which is really too low for "optimum" off grid use--The sun is just not in the sky that many hours per day for fully recharge a 50% discharged GEL battery).
The caveat here is that there are many different GEL battery designs/manufactures--Again fall back to the manual and make sure you meet their requirements vs the above generic recommendations.
For MPPT controllers--The typical "max current" calculation for charging current (the most current you will see for a few hours on a cool/clear day during solar noon, a few times a year):- 400 Watt array * 0.77 controller+panel deratings * 1/28.4 volts battery charging voltage = 10.85 Amps usual "max" current for MPPT system
- 200 AH * 0.05 (5%) suggested rate of charge = 10 amps "generic" max charging current
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
It's not clear whether you're putting together a 24V system, or a 12V one with an MPPT controller.
Some controllers (e.g. Morningstar Prostar MPPT) have a setting to limit max charging rate. -
Hi Bill and Mike, thank you for your responses!
Mike - I'm building a 12V system but want to use a 24V panel as i can afford a much better quality one if I do so.
Bill - thank you for your explanations. I think I follow for the most part, though I'm a little lost at the end. If I understand well, your advice is firstly to use an AGM rather than a GEL?
Thereafter, I am slightly confused (sorry). Here's what I've understood:
-The battery charing voltage (28.4V) comes from two 12V, 200Ah batteries wired in parallel and their volt set points.
-The 0.77 is the effiiency of the 400W solar array.
-The 5% rate of charge is the rate at which a GEL battery can safely be charged at (I'm seeing that figure at 20% for AGMs?)
What i dont understand is the "max current" (10.85A) for the MPPT system as in my (clueless) mind, the calculation seems to use the oanel details and then the battery details. Unless this means that the maximum current that will ever need to go through the MPPT is 10.85A?
Furthermore, I dont understand the discrepancy between the max charging current calculation (10A) and the specified max charging current on the battery spec (37.5A).
Bearing all that in mind, if I go for 400W, 12V panel and 2x 155Ah, 12V AGM Batteries. What MPPT CC would I need?
Sorry for my rudimentary ignorance. -
@Asinnobooks
To do a rough calculation take the panel wattage and divide by the nominal voltage, 400W ÷12V = 33.3A, in reality it will likely be around 25A therefore a 40A controller would be a good fit, but pay attention to the final paragraph.
An MPPT controller will accept a higher voltage than the battery and convert the excess voltage to increase charging current at the lower voltage the battery requires, the power output of the panel won't be increased by the MPPT controller. In most cases panel output will be less than the Standard Test Conditions (STC) usually in the 70-80% range. This link explains in detail how MPPT controllers work https://www.solar-electric.com/learning-center/mppt-solar-charge-controllers.html/
There are batteries which are referred to as GEL in Europe that are deep cycle, the term differs in North America where GEL refers a standby type battery not designed for regular cyclical use, consult the manufacturer for details.
Two 12V 200Ah batteries in parallel with a maximum charging current of 37.5A each current would be doubled to 75A or roughly 18% of total Ah capacity, using the 25A value from above the charging rate with a single 400W panel would be 6.3% which is pretty low, however to build a ballanced system one would begin with loads, then the battery capacity needed to support them and finally the PV required to replenish the withdrawals.
It would appear that you're actually starting midstream, which is a fundemental mistake many make, doing things right the first time will save you the headache and expense of loosing the batteries prematurely due to cronic undercharging. My suggestion is to rewind to the beginning and design something that will work, perhaps with a new post to eliminate confusion.
1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
Thereafter, I am slightly confused (sorry). Here's what I've understood:
-The battery charging voltage (28.4V) comes from two 12V, 200Ah batteries wired in parallel and their volt set points.
-The 0.77 is the efficiency of the 400W solar array.
-The 5% rate of charge is the rate at which a GEL battery can safely be charged at (I'm seeing that figure at 20% for AGMs?)
I had guessed you were doing a 24 volt battery bank (2x batteries in series). In fact, you are doing 2x batteries in parallel. So the correct equation for a 12 volt battery bank would be:- 400 Watt array * 0.77 controller+panel deratings * 1/14.2 volts battery charging voltage = 21.7 Amps usual "max" current for MPPT system
- 400 AH * 0.05 (5%) suggested rate of charge = 20 amps "generic" max charging current (for US GEL batteries)
Note that the energy stored from two batteries series vs parallel connected store the same amount of energy. Just deliver it at different battery bus voltages:- 2 * 12 volt series batteries * 200 AH capacity = 24 volts * 200 AH = 4,800 Watt*Hours (stored energy)
- 12 volt battery * 2 parallel * 200 AH capacity = 12 volts * 400 AH = 4,800 Watt*Hours (same stored energy)
The ~77% derating is because "Hot" solar panels have lower Vmp (voltage maximum power). And MPPT controllers are "constant power devices (ignoring losses):- Parray = Vmp * Imp (solar array voltages) = Vbatt * Ibatt (battery side of controller)
We use rules of thumbs here a lot... This is to make the design process much simplier and quicker to a reasonable design without going through each of the details.
If you wish to better understand the details, we can certainly go into them.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
@mcgivor - thank you for your response. Believe it or not i actually thought i was starting at the beginning here. I have identified that I need about 120-130Ah per day maximum and after looking around online, came to the conclusion that approx. 300Ah of AGM or GEL (I'm in europe) batteries would do the job and that 400W of solar power would be sufficient for charging. (I will also connect the batteries to the van battery's alternator). That's been my thinking hitherto, what would you advise is order to "rewind"? I definitely don't want to make any mistakes in planning this and am keen to do it the right way.
@BB. - thanks again. Some of those calculations are making more sense now, though I you lost me with this:- Parray = Vmp * Imp (solar array voltages) = Vbatt * Ibatt (battery side of controller)
I guess my questions concern, in essence, what the next steps are and ultimately what i need to purchase if the 400W 24V panel array and 2x 155Ah, 12V AGM batteries (or perhaps GEL if the fact that I am in Europe means that they are actually suitable [they are less expensive!]) work together.
I'd definitely like to understand better the details, as you suggested, as I don't want to go into this without a full understanding. I'm just really starting with no technical knowledge and all the acronyms etc are still extremely confusing and overwhelming. Thank you so much for your help!
-
Starting with the "technical questions".... Solar cells are NOT solar batteries.
We are all pretty familiar with what a battery is... More or less a battery holds 12 volts from zero to maximum current (Amperes). A "constant voltage" source.
Solar panels, for the most part, are "constant current sources". If you have an Imp = 10 amps solar panel (current maximum power)... Under full sun the panel will (for a first approximation) output 10 amps from zero volts to Vmp (voltage maximum power).
Say you have a Vmp=35 VDC for your panel (we need to know the details, Vmp and Imp at least for your panel(s)). Then we look at the equation for power:- Power = Voltage * Current
- Power panel = Vmp * Imp = 35 VDC * 10 Amp = 350 Watt "rated panel"
- Power from panel = Vmeasured * Imeasured = 12 volt battery * 10 amps = 120 Watts
- Power from panel = 0 volts (dead short) * 10 amps = 0 Watts from panel
- Panel output hot summer day = Vmp * temp derating * Imp (Imp does not change much with temperature
- Panel output hot summer day = 35 Vmp(std) * 0.80 temperature derating * 10 amps = 280 Watts from panel to MPPT controller (derated for "normal operation" conditions)
So... when in "bulk charge" mode (the MPPT controller is outputting maximum power to a discharged battery), the Power into the MPPT controller is about the same as the power out... Say 280 Watts is available from my imaginary solar panel, then charging a 12 volt battery bank:- Power = Voltage * Current
- Current = Power / Voltage
- Current into battery = Psolar / Vbatt
- Ibatt = 280 Watts (hot panel) / 12 volts charging "very discharged" battery = 23.3 amps into battery (less than 50% charged)
- Ibatt = 280 Watts (hot panel) / 14.2 volts charging "80% full" battery = 19.73 amps into 80% charged battery
Here is a thread that discusses about understanding solar panels:
https://forum.solar-electric.com/discussion/5458/two-strings-in-parallel-with-unequal-string-voltages
And, an FAQ that has lots of links to various solar/battery/conservation discussions. See if there is anything of interest:
https://forum.solar-electric.com/discussion/4426/working-thread-for-solar-beginner-post-faq/p1
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Document your system design:
- 2x 12 volt @ 200 AH batteries for a 12 volt @ 400 AH battery bank
- 400 Watt @ "24 volt" solar panel (that could be Vmp from 24 volts to 36 volts or so
- 130 AH @ 12 volt day "max loads"
- 40 Amps (*) MPPT charge controller
- Location--Perhaps somewhere around Lyon France(?)
1 day discharge and 50% max discharge or 2x daily load storage can work OK for weekend/sunny weather use... For full time off grid, suggest 2 day storage + 50% discharge or 4x daily load (lead acid batteries take several days to fully recharge if discharged deeply).- 400ah/130ah= 3.1 x storage capacity
Next, charging... Normally suggest a minimum of 5% rate of charge for weekend/sunny weather system. 10-13% minimum for full time off grid daily use/year round system:- 400 AH * 14.2 volts charging * 1/0.77 solar panel+controller deratings * 0.05 rate of charge = 369 Watt minimum array
- 400 AH * 14.2 volts charging * 1/0.77 solar panel+controller deratings * 0.10 rate of charge = 738 Watt array nominal
- 400 AH * 14.2 volts charging * 1/0.77 solar panel+controller deratings * 0.13 rate of charge = 959 Watt array "typical" cost effective maximum
For an array facing south in Lyon:
http://www.solarelectricityhandbook.com/solar-irradiance.htmlLyon
Measured in kWh/m2/day onto a solar panel set at a 44° angle:
Average Solar Insolation figures
(For best year-round performance)
If you "toss" the bottom three months (winter) and only use the system 9 months a year:Jan Feb Mar Apr May Jun 2.18
3.01
4.06
4.39
4.74
5.13
Jul Aug Sep Oct Nov Dec 5.52
5.23
4.45
3.07
2.20
1.74
- 130 AH * 12 volts = 1,560 Watt*Hours per day
- 1,560 WH per day * 1/0.61 DC off grid system eff * 1/3.01 February "break even" = 850 Watt array for February "break even" operation
Your thoughts?
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
Categories
- All Categories
- 221 Forum & Website
- 129 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed