solar
Plucka
Registered Users Posts: 130 ✭✭
I have 360 amp/hr 12 volt lithium battery bank which feeds through 2500 watt 240 volt inverter and I'm thinking of buying a aircon for cooling that states it is 1600 watt 240 volt.The question is how long would the battery last with the solar panels charging at 40 amps for 5 hours -less for rest of the day ? I hope to get 5 hours aircon during the day, off at night .
It depends... I think I have read here that there are some nice Mini-Split inverter units that can run at 300 Watts (low)--Start earlier in the day (on low), and bring temp down/keep cool for evening. Other/larger AC units can easily run 1,000 watts or more.
Say you want 8 hours per day (4 hours afternoon, and 4 hours evening):- 300 Watts * 8 hours * 1/0.85 AC inverter eff * 1/12 volts battery bus = 238 AH per cycle @ 12 volts
- 300 Watts * 4 hours evening * 1/0.85 inverter eff * 1/12 volts = 118 AH @ 12 volts
NOTE: Updated below--Fingers got ahead of brain. -Bill- 360 AH * (0.90-0.20) = 252 AH "usable" AH capacity
- 40 amps * 12 volts = 480 Watts
- 40 amps * 5 hours charging = 200 AH per day
- 40 amps * 5 hours * 14.5 volts = 2,400 WH per day
- 2,400 WH per day * 0.85 AC inverter eff * 1/300 Watt load = 6.8 Hours of estimated runtime
300 Watts is probably at the very low side of A/C power usage...
Hopefully, somebody else here can give you some actual hardware, numbers, and how to operate.
thanks Bill
You are very welcome.
By the way, click on link below (duckductgo.com) or put the search term into duckduckgo or google:
https://duckduckgo.com/?q=site:https://forum.solar-electric.com/+300+Watt+mini-split&ia=web
"site:https://forum.solar-electric.com/ 300 Watt mini-split" (search tag "site:" and term limiting to our forum)
And can see some older (and newer?) posts referencing 300 Watts on a Mini-Split.
The actual run wattage will be determined by the demand, cheap single speed units are all or nothing, running at maximum power until the setpoint is met. High efficiency inverter units may initially run at full power then slow the compressor down, top of the line may be programmed to run on ECO mode, so there is no definitive answer. My Diakin 9000 btu is substantially more efficient than a similar Samsung but cost twice as much, both inverter type, Diakin has a linear compressor and R 32 refrigerant as opposed to rotary with R 410A, it's consumption can be as low as 165W.
The thing to consider is what the battery current will be when running at full power, 1600W ÷ 240V is 6.66A at 240V, the battery being 12V nominal will need to support 133.3A with the 20:1 ratio, 240V ÷ 12V, not including inefficiencies. The array would need to be sized not only to recharge what was depleted from the previous cycle but support the A/C as well.
From an outside perspective it would seem unlikely to achieve with such a diminutive system, consider a swamp ( evaporative )cooler if there is low humidity.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS