Schneider Conext SCP Firmware Update - Power Readings Issue

I recently updated the firmware on my Schneider Conext SCP (SKU 865-1050-01 to the most recent firmware (Schneider Conext SCP2.04 APR 2018 to V2.05 JAN 2021) downloaded from the Schneider Electric website. I successfully uploaded the firmware via the Combox, but now when I use InsightCloud or login via a browser to my Combox, I no longer get any readings from the solar input (MPPT60/150) nor can see my actual load consumption. I also noticed that I can no longer see the solar power generation nor the current load on the SCP display
Any suggestion on how I can get these readings back? I have already tried to reboot the system and I have even reinstalled the firmware to V2.04 and I can't resolve the issue.
Any suggestion on how I can get these readings back? I have already tried to reboot the system and I have even reinstalled the firmware to V2.04 and I can't resolve the issue.
Comments
http://members.sti.net/offgridsolar/
E-mail [email protected]
The SCP does not show solar input or loads without combox on xanbus? That would be really weird!
What about devices, are they there?
What else is in the system? Is this offgrid? Where are you? More info will make this easier?
http://members.sti.net/offgridsolar/
E-mail [email protected]
SW4048 120/240
MPPT 60/150
SCP
Battery Monitor
Combox
I have 2 banks of L16 Duracell Batteries (48V setup)
I checked the Xanbus cables and all are in perfect condition, no corrosion nor wear or tear. The Combox, SCP and the Battery Monitor are all installed inside an electrical cabinet and the Combox is connected to the internet via a ethernet cable to my router (see photo below)..
This system had been up and running for two years now with no issues whatsoever until now.
This issue started after I updated the SCP firmware as mentioned in the first post of this post string.
All units are being detected by the Combox and there is no error (see photo below).
I am thinking that perhaps the SCP failed when the firmware update was being performed. It hanged once the first time I updated the firmware; I powered the system off and on, then I managed to update the firmware as described in my posts above. No other firmware was updated (only the SCP)... perhaps it has "bricked"
Also look in SCP system screen, scroll to the end and note any faults or warnings, one down from faults. Any on the day you did the firmware? I do not think you can say the SCP is bricked. Not sure that can happen either.
I assume you have wiggled all of the network cables in case there is corrosion in PR. It would not be the first time they look good but
I would disconnect all of the networking and just plug the SCP in with the mppt during daylight hours, then add the inverter, or do the opposite. When you powered down the DC, you shut down the solar in and let the system sit for 5 minutes or so. The DC on the CSW needs to be at zero volts DC.
Xanbus connection issues from Schneider below.
Resolution:
Make sure Xanbus ports are being used throughout the system including the Terminator at each end of the daisy chain. Make sure to use known good Cat5e cables (standard Ethernet at least 6ft long). Try connecting one unit at a time while verifying unit appears on device list of SCP.
Good Luck ! You need to isolate things. This can be a pain I know. Why did you do this if your are offgrid?
http://members.sti.net/offgridsolar/
E-mail [email protected]
The cables have all been checked, but I will recheck them. I have most of the instruments in a enclosure to avoid corrosion (only the MPPT and the Inverter are on the wall). I have two temp sensors installed in my system, one of them is connected to the SW4048, the other one is connected to the MPPT. I'm not sure if it is alright to have more than one connected on the same system, but they have been connected since the day I installed the system and have never caused a fault.
.
Since you know the battery monitor is getting data out to SCP, that is your starting point. Add one device at a time and leave combox for last. Everything is working right, powering loads? You are offgrid? Need those answers manyana! Buenos Suerte!
http://members.sti.net/offgridsolar/
E-mail [email protected]
Thanks again for you advise, I will check it out as soon as I can!
Question: I have a few cables that were custom made (shorter than 6ft) because the enclosure I have is quite small and I wanted to keep it as uncluttered as possible. I did this because I had read online that cable length does not affect the cables' operation; but others say that the cables should be 6' long (Dave also mentioned this, see above). Does anyone have any negative experiences using shorter cables for Xanbus? Do all Xanbus cables have to be of the same length? Note: the short custom cables were installed when I first installed my system and I had never had an issue with them until now.
I plan on isolating the Xanbus units and cables one at a time as Dave suggested (see above) later this week hoping to isolate the defective cable or unit. I will post the results of this testing. I also ordered an inexpensive cable tester as I currently don't have one. Hopefully I can finally resolve this issue one way or another.
The mean season is coming, better get this thing working! Good Luck!
http://members.sti.net/offgridsolar/
E-mail [email protected]
I have a combox and insight home. both are receiving very limited info.
It's been a long time since the system was commissioned,