FM 80 shows "Charged" but won't go to float
RanchoPacifico
Registered Users Posts: 7 ✭✭
I recently changed my battery bank to LiFepo 4 batteries and ever since then I have been noticing that my fm80 will sometimes work fine and go to float after the batteries finish absorb at 58v and float at 56v. But about every 3 days after absorb the CC shows "charged" and won't go to float. Anyone else seeing anything like this?
Off grid in northern Baja, 2- vfx3648, FM80, 2280 w pv array pole mounted with solar trackers, 300ah LiFepo4 battery bank, Kubota 6.5kw Diesel gen.
Comments
-
Aaaaa I don’t think the liFepo battery’s go thru absorb when charging with a fm 80 you need to really check that out .Charged pops up when my battery’s time out of absorb and the controler says charged until the battery get down to float voltage then changes to floatOut back flex power one with out back 3648 inverter fm80 charge controler flex net mate 16 gc215 battery’s 4425 Watts solar .
-
I know not to absorb lifepo batteries but since the fm80 started acting up I thought that maybe the fm80 needed a little absorb time to go to float so I set absorb time to .1 hour hoping it would go to float but so far it works sometimes and not others. After thinking about it for a day I'm wondering if my bms is shutting my batteries off and the fm80 doesn't know what to do so next I'll try lowering the absorb voltage a .1 lower to 57.9v for .1 hour. and see what happens.Off grid in northern Baja, 2- vfx3648, FM80, 2280 w pv array pole mounted with solar trackers, 300ah LiFepo4 battery bank, Kubota 6.5kw Diesel gen.
-
If your battery bus "goes away" because of BMS shutdown... Review the battery specs and BMS logs (if present/accessable) and see why the BMS made that decision.
BMS shutdowns should be a a very rare event and I don't like to cut the battery bank out of a DC system/circuit. The battery bank is what actually "regulates" the Battery Bus voltage (holding it between ~42 and ~60 volts). Solar charge controllers, alternators, etc. are not usually designed to actually output regulated 5x.x volts and with the battery gone, the charging sources can frequently over voltage in a fraction of a second and possibly damage other loads/charging sources on the battery bus (car alternators/wind turbines can easily exceed 100 volts, and solar charge controllers can spike to near Vmp-array voltage).
And if you do "lose the battery", you should shut down the solar array(s) to your solar charge controllers, and turn off the DC battery connection... Wait a minute, then FIRST connect the DC bus and let the charge controller boot and stabilize, then connect the solar array next. If the charge controller is powered by the array first, it can get confused and not boot correctly (or even damage itself).
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Charged is a product of your voltage
when I hit my 3 hour absorb the fm80 go to charged when the voltage gets to my float voltage 54volt the controler go’s to float .
I think the lipo battery’s get 2 stage charging at first you have x amp till you get to x volt then constant volts till you hit the charged voltage number .I’m sure one of the wizards on the board will chime on soon I wish I could be of more helpOut back flex power one with out back 3648 inverter fm80 charge controler flex net mate 16 gc215 battery’s 4425 Watts solar . -
This has a really good Explanation as to how to
set the fm80 up to charge you just need to in put your voltages
Out back flex power one with out back 3648 inverter fm80 charge controler flex net mate 16 gc215 battery’s 4425 Watts solar . -
This has come up before, it's the transitional period between when the absorption ends and the time it takes for that voltage value to drop to the float value. Because LFP battery voltage dose not drop rapidly once the charging is terminated, unlike LA dose, the length of time the display reads charged will be extended in comparison.
To verify this, apply a load to reduce the battery voltage to the float value, whereupon the display will change to read float.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
I agree, that seems to be exactly what is happening but on a few occasions I have not noticed the "Charged" notification until late in the afternoon and by then the voltage is down below the float voltage by about 4 volts (52v) and the fm80 didn't switch to float at 56v as it should have. As I said previously this "charged" notification doesn't happen everyday only once every 2 or 3 days. I've been using this fm80 for about 8 years and an mx60 for 10 years before that so I am not new to the Outback CC and have never seen my charge controllers do that. I still have my mx60 so maybe I'll try removing the fm80 and putting the 60 in its place and see if the problem goes away.Off grid in northern Baja, 2- vfx3648, FM80, 2280 w pv array pole mounted with solar trackers, 300ah LiFepo4 battery bank, Kubota 6.5kw Diesel gen.
-
Are you running the fm80 thru a mate ?My system started getting freaky last year at this time . For no reason the controller stoped
Absorb after a hour ?Then I would see charged with out float
then the next day it would work ?I never updated the firm wear .Once I did the up dates and reprogrammed it
The system has been working real good
Maybe you need up dates ?Out back flex power one with out back 3648 inverter fm80 charge controler flex net mate 16 gc215 battery’s 4425 Watts solar . -
Yes I am running through a mate2 the older mate. I'll check on if there are updates available. I did some changes today and it went from absorb to float as it should. We'll see what happens tomorrow.Off grid in northern Baja, 2- vfx3648, FM80, 2280 w pv array pole mounted with solar trackers, 300ah LiFepo4 battery bank, Kubota 6.5kw Diesel gen.
-
My system went screwy
I’m not the kind of guy that pushes buttons
My system changed buy it self , very strange since I’m not connected to internet
I did a update on my inverter and that fooled with my genarator charging ?I’m getting less charging 1700watts vs 1900watts and don’t know why .But it works it just take a little longer to charge.My system is 4 years old and there where
4 updatesOut back flex power one with out back 3648 inverter fm80 charge controler flex net mate 16 gc215 battery’s 4425 Watts solar .
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 189 Solar Information links & sources, event announcements
- 886 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed