Pwm showing different v than multi meter
Streatwise
Registered Users Posts: 7 ✭✭
Just installed basic pwm controller and solar panels in my van. The battery is fully charged and is showing 13.8 on multi meter, tested on wires going into pwm. The pwm display is showing 12.7 v.
Any thoughts if this is a faulty pwm or if its a setting wrong?
Thanks for any advice
Any thoughts if this is a faulty pwm or if its a setting wrong?
Thanks for any advice
Comments
-
Take the voltmeter to your car and see if it around 12.8 volts with the engine not running and around 13.8 to 14.4 volts when the engine is running.
Your voltmeter is probably fine, but I have seen DMM (digital multimeters) give some very strange readings if the battery is near dead (and no on-screen battery warning warning).
Some higher end meters do allow for adjustments to meter readings.. But very few lower end system meters/solar charge controllers do--And a 1.0 volt difference is not something to 'paper over'.
Sometimes, you can get variations in meter vs actual readings--Some vendors will display a temperature corrected battery voltage meter reading for the battery bank... For example, if there is a -0.005mv/C/Cell offset, and your system is at 35C (95F):- -0.005 volts * (35C ambient - 25C standard temp) * 6 cells (12 volt battery) = -0.30 volt "depression" in charging voltage for "hot" battery
One other slight chance for errors... You always want to connect the DC Battery to the controller first, then connect the solar array. If you connect the array first, and then the battery bank, the charge controller can get confused during booting (and in some cases a connected/in sun solar array without battery bank connected can damage the charge controller). So, to reboot the charge controller: Disconnect solar panel first, then disconnect battery wiring to charger--Wait 30 seconds--And then connect battery bank first, then solar array second.
Assuming your DMM is correct and the solar charge controller is wrong--It sounds like you need to call the vendor for more help or a replacement. At this point you do not know if this is a "display issue" (LCD is telling you the wrong voltage) or a problem where the controller is "seeing" the wrong voltage and will not properly recharge your battery bank).
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Hi Bill
Thanks for the advice. Pretty sure my DMM is correct but will test again against a battery.
All being well will disconnect battery and pvc from the controller then reconnect a x test again see if it resets.
Will let you know how it goes, weather permitting as its broken today and raining.
Cheers
Aaron -
Streatwise said:The battery is fully charged and is showing 13.8 on multi meter, tested on wires going into pwm. The pwm display is showing 12.7 v.
In any case, the input and output of a PWM controller may not be a simple DC voltage. There can be a PWM component (basically, AC on top of DC), which may confuse a simple meter. -
What Mike _S talks about could be an issue if there are bad electrical connections or too small of wire from charge controller to battery bank.
Checking the voltages when the sun is "down" should show both Meter and DMM with the "same numbers". And you can do a quick check with the system charging (current flowing) by using the DMM to measure both the terminal voltage on the Vbatt output of the controller, and on the battery(ies) terminals themselves. In an ideal system, with full charging current, the voltage drop from Vatt-terminals to Vbus should be 0.10 volts or less (for a 12 volt system).
There can be issues with "simple" digital meters that "sample" once a second or so the voltage vs True RMS (root mean square) DMM meters. With a PWM output, it is possible for the meter to be sampling "peak" voltage of the PWM (pulse wave modulation) vs the "average (RMS) voltage. It is not a common issue--But if combined with "problematic wiring" is certainly possible (checking voltage at night would bypass this issue).
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Hi Both
Well following my last post I have reset controller... disconnected solar array, then battery, left 1 min and connected back up again. Have float set to 27v and no load attached, only used to keep battery charged for when needed.
Have attached pictures of afterwards.
1st pic is display on PWM, the 2 probes are my DMM on the wires to the battery. So PWM is reading 12.6v.
2nd pic is my DMM show a reading of 13.03v (it did fluctuate between 13.2 and 13.5 while probes were in place)
3rd picture is probes on the solar array input
4th pic is the reading from this (have 2 20v pv panels in parralell) sun was going down so is quite a low reading.
So after resetting I still get a different reading on the controller display of float charge state to the reading onmy DMM.
Maybe this is just because the controller is a cheap model, but thought it woukd still give an accurate votage reading.
Anyway any thoughts much appreciated
Thanks
Aaron -
Thy replacing the battery in the DMM, this may affect readings and I believe the meter is telling you to do so by the battery icon1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
Did you measure the battery terminal voltage on the batteries themselves?
The solar panel voltage should be a little bit higher than the battery terminal voltage (to ~20 volts). Current flows "down hill"--So the panels have to be the same or higher voltage than the battery terminals.And as McGovern says, try a new meter battery.BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Thanks guys
Will try battery replacement on my DMM and see how that goes.
Yes I did test on tbe actual battery terminals and DDM gave same reading as above 13.03v
The reading from my panels was low as this picture was half hour before sunset, during the day they normally show as giving between 15 and 20v.
Cheers
Aaron -
"Well following my last post I have reset controller... disconnected solar array, then battery, left 1 min and connected back up again. Have float set to 27v and no load attached, only used to keep battery charged for when needed. "
Why is the float set to 27 volts?2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
I have set the float to 27v as didn't want to over charge the battery, seeing as the metre is reading a higher voltage than the controller I was erring on the safe side until I figure out what's going on...
-
I think the question was more 27 Volt Float with a 12 volt battery bank? Nominally float is around 13.6 volts or so for a 12 volt bank...
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Sorry my mistake... That meant to say float set at 12.7v not 27v...
-
No problem... Everyone just wants to make sure to keep safe.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Ok so update on this issue..
Replaced battery in DMM, also got new probes as the ones in use were a bit knackered.
Now only showing a +0.2v difference to the charge controller display...
Keeping an eye on it but hopefully this was the issue..
Cheers all
Aaron -
Probably the tollerance of the metering is responsible for the deviation, I would think the meter is more accurate because it likely has a higher resolution and tighter tollerance than a charge controller, good to know you've sorted it out.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
Categories
- All Categories
- 220 Forum & Website
- 128 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 189 Solar Information links & sources, event announcements
- 886 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed