How many panels can I have with an...?

Registered Users Posts: 2

So looks like I need a little help with interpreting the numbers on my charge controller to figure out how many panels I can add.

I have an EPEVER Tracer 3210A MPPT charge controller, and the numbers on this thing indicate a max PV input of 100V and current of 30A. It also indicates that max PV input power is 390W@12V, 780W@24V. This tracks as 390W/12V=32.5A=780W/24V. Where I'm getting hung up is, what if my PV input voltage is closer to the max voltage of 100V? would this mean the controller can handle a max PV input power greater than mentioned above (390W@12V, 780W@24V). Say I wanted to run a series-parallel array that was 880W@75V (~12A)? This voltage is less than the max input voltage and below the 30A current.

Any help would be greatly appreciated. Thank you for your time. 

Welcome!

It looks like you're new here. Sign in or register to get started.

Comments

  • Solar Expert Posts: 6,017 ✭✭✭✭✭
    The current is based on the output of the controller, So a 880 watt input (within their specs) Would output around 880/12=73 amps too high for 12 volt system. or 880/24=36.6 too high for a 24 volt system. Some MPPT charge controllers can be 'over paneled' and you just lose the extra available wattage. I don't know if that's true of the EPever, it does look like it's somewhat true as they list a higher max array;


    Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites,  Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
    - Assorted other systems, pieces and to many panels in the closet to not do more projects.
  • Registered Users Posts: 2

    Thank you.

    So since I'm charging a 12V system, I should keep my panels under 580W? And this will help when panels aren't putting out 100% of their capabilities?

  • Solar Expert Posts: 6,017 ✭✭✭✭✭
    Solar_5th_Wheel_ said:
    So since I'm charging a 12V system, I should keep my panels under 580W? And this will help when panels aren't putting out 100% of their capabilities?
    That's the way I read it.
    Looks like I got the manual for the 3210AN rather than the 3210A, so might hunt down the proper manual.

    Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites,  Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
    - Assorted other systems, pieces and to many panels in the closet to not do more projects.