Trying to Power a 1/2 HP Booster Pump and already killed a battery
claywd
Registered Users Posts: 6 ✭✭
I have this booster pump which fills a pressurized tank indoors with water stored in my outdoor storage tank. It only runs for a minute or so max maybe two to three times a day. My Idea was to power it with four of these batteries in parallel to create a higher throughput amperage using 4AWG wire. Charging the batteries was trivial so we won't focus on that part. I'm using this inverter for output.
Context:
Well my original calculations said that one of the batteries would power the pump for at least 10 seconds so I hooked it all up and gave it a go. The pump kicked on for about 1/2 -1 second and then it all died.... I disconnected the battery, hooked it up to a charger real fast and everything seemed fine. So I tried it again thinking maybe something came loose. This time, the pump didn't power up. The battery also doesn't take a charge anymore. That being said, I figured I must have overlooked some detail and need to provide more power. So I ordered more batteries... determined to make this work.
Problem.
I ran across a forum where someone was calculating something similar to what I needed to calculate and I think its saying I need to be able to provide 5 x 11 amps @ 230 volts = 12,650 watts for starting the booster pump at least for the first few seconds. Well, that's 12,650/12vdc= 1054A.... If all this is correct then...
Context:
Well my original calculations said that one of the batteries would power the pump for at least 10 seconds so I hooked it all up and gave it a go. The pump kicked on for about 1/2 -1 second and then it all died.... I disconnected the battery, hooked it up to a charger real fast and everything seemed fine. So I tried it again thinking maybe something came loose. This time, the pump didn't power up. The battery also doesn't take a charge anymore. That being said, I figured I must have overlooked some detail and need to provide more power. So I ordered more batteries... determined to make this work.
Problem.
I ran across a forum where someone was calculating something similar to what I needed to calculate and I think its saying I need to be able to provide 5 x 11 amps @ 230 volts = 12,650 watts for starting the booster pump at least for the first few seconds. Well, that's 12,650/12vdc= 1054A.... If all this is correct then...
- I can't supply that over 4awg... at least not for long
- The inverter I chose won't work for powering anything above 5k watts and I might have blown it as well.
- idk if batteries can discharge that fast but I figured one battery should be able to provide 72kA/s or 1kA for a minute. So I don't fully understand why the battery died.
Comments
-
Claywd, are you trying to repost your question (the software put you post "in moderation" because it looked like a duplicate post?
Any, if you want to continue, we can... Or I can delete.
Take care,
Bill "moderator" B.Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Also, should I just abandon the plan to run this well pump and instead invest in something like this? Tankless Pressure Pump™ System - NEW 2019 – RPS Solar Pumps
I feel stupid for not looking into the above sooner... 🤦♂️ -
BB. said:Claywd, are you trying to repost your question (the software put you post "in moderation" because it looked like a duplicate post?
Any, if you want to continue, we can... Or I can delete.
Take care,
Bill "moderator" B. -
What batteries are you using?1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
No problem. I can move your post, you don't have to repost... And we are pretty easy going anyway.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
mcgivor said:What batteries are you using?
-
There are a few things that need to be considered, first the battery is far too small to power the pump, most likely what's happened is the internal BMS has disconnected the load on overcurrent, this will also in effect disconnect the ability to charge.
The pumps AC current demand has to be multiplied by a ratio of 20:1 for a 12V battery, roughly the run current should be ~4.6A, therefore the battery needs to supply 92A at 12V and significantly more on startup, perhaps 400Ah for a second or so. The 80Ah bank should have a maximum 80A, or 1C for each 24Ah.
Using a smaller pump is one solution, or a larger battery capacity, but 12V inverters are not user friendly and really shouldn't me made at such high wattage due to the high currents needed, moving up to 24 or 48V would be best.
1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
I agree on the 12v setup. The batteries are so readily available though and I was hoping to make this adaptable in case it didn't work and I went with a different setup altogether. I could at least reuse the system for something else. I'll keep the 24V/48V option around as well while considering all the options.perhaps 400Ah for a second or so. The 80Ah bank should have a maximum 80A, or 1C for each 24Ah.So if I were going to build the minimum system I would need another 14 batteries to make up the missing 320Ah required to turn that pump on?
-
Having 18 batteries in parallel is not a wise idea, many connections and hard to ensure each is charging or dischargeing at equal rates. A better solution would be to have a single battery with one BMS, usually made-up from large capacity prysmatic cells something like this
https://www.amazon.com/Lifepo4-Lithium-Battery-System-battery/dp/B07TWDP8D9/ref=sr_1_32?dchild=1&keywords=200+ah+lithium+ion+battery+24v&qid=1613721973&sr=8-32
Actually works out cheaper as well, I linked a 24V 200Ah example, same cost for 12v 400Ah.
Whenever using solar it's best to have equipment like a pump working during sunlight hours, keeping it as small as practical, having a 1.5 hp pump working for a few minutes per day, or night, requires electrical support equipment to be sized accordingly. For example I recently installed a submersible 24V DC well pump with is own MPPT controller that is powered by a single 400W panel without batteries , it can fill a 1000 liter (260 gallon) holding tank in 2 hours in perfect conditions, a second 230V 150W on demand pump provides house pressure, everything including the demand pump cost ~$400.
Not knowing exactly what your particular requirements are I can't offer suggestions, other than to say, I think you need to rethink the whole exercise, there must be a better solution.
1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
mcgivor said:Having 18 batteries in parallel is not a wise idea, many connections and hard to ensure each is charging or dischargeing at equal rates. A better solution would be to have a single battery with one BMS, usually made-up from large capacity prysmatic cells something like this
https://www.amazon.com/Lifepo4-Lithium-Battery-System-battery/dp/B07TWDP8D9/ref=sr_1_32?dchild=1&keywords=200+ah+lithium+ion+battery+24v&qid=1613721973&sr=8-32
Actually works out cheaper as well, I linked a 24V 200Ah example, same cost for 12v 400Ah.
REC TwinPeak 2 285W 3S-3P 2.6kW-STC / 1.9kW-NMOT Array / MN Solar Classic 150 / 2017 Conext SW 4024 Inverter latest firmware / OB PSX-240 Autotransfomer for load balancing / Trojan L16H-AC 435Ah bank 4S connected to Inverter with 7' of 4/0 cable / 24 volt system / Grid-Assist or Backup Solar Generator System Powering 3200Whs Daily / System went Online Oct 2017 / System, Pics and Discussion
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed