grounding
dougahole
Registered Users Posts: 13 ✭✭
The charging system. Off grid, Honda e7000 generator, AIMS 4KW inverter. Generator is grounded at site, cable runs directly to inverter (grounded) as ac input, output from inverter to panel and grounded at panel. Inverter will not accept in coming power from generator. What is wrong with this picture? I am led to believe that it is a grounding problem but do not know how to correct it. Can someone provide a diagram and/or recommendations. Thanks
Comments
-
Not really familiar with your equipment but usually you only want a system grounded in one location, typically at the panel. Have you tried lifting the generator ground and seeing what happens - at least that would let you know if grounding is an issue. Are there any ground fault circuits on the panel, generator or elsewhere? They can get confused with two grounds. Also, you need to check how your neutral is wired. There are many posts on proper neutral connections and bonding of neutral to ground (again usually only in one place, at panel). Sometimes generators come bonded and sometimes they are not so best to check.
Offgrid in cloudy PNW
Full Schneider system with 18 REC 420W panels, 100A-600V controller, XWPro, Insight Home, six Discover AES Rackmount 5kW batteries, Slimline enclosure, Lynk II, AGS, H650, H2200, H3000 (On Victron AutoTrans with Gen Line 2 wire AGS on AC1), Kubota 4500, Onan 7500 (on second AGS and AC2).
-
Is this the same problem from November of last year which is unresolved? The internal neutral ground bonding required by OSHA for use on job sites most likely is the issue, the pdf attached explains how to remove the bonding when using a transfer switch, which an inverter charger has, it's a little dated and perhaps doesn't cover you exact model, but still relevant.
Also heed the advice from @Graham Parkinson above.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed