Generator Charging Issues
Good Morning,
New to this technolgy so please bear with me if I don't know all the lingo.
I am working with an off grid system.
(2) XW5548 Inverters
XW SCP
XW AGS
Com Box
Conext Battery Monitor
Kohler 14RESA Generator
Batteries (830 AH)
My problem is the following:
Generator starts as required by the trigger setting, the inverter is reading about 1.5KW (lights and various loads) with the AC2 LED lamp flashing and then switches from reading KW to Amps on the front panel and rises to around 99Amps and shuts down and resets and starts this over again.
The other issue I have is that I can hear the generator change speeds when the above happens and after a couple of times the generator with go off on a faulure of Low Frequency.
Please let me know your thoughts.
Thanks Dan
New to this technolgy so please bear with me if I don't know all the lingo.
I am working with an off grid system.
(2) XW5548 Inverters
XW SCP
XW AGS
Com Box
Conext Battery Monitor
Kohler 14RESA Generator
Batteries (830 AH)
My problem is the following:
Generator starts as required by the trigger setting, the inverter is reading about 1.5KW (lights and various loads) with the AC2 LED lamp flashing and then switches from reading KW to Amps on the front panel and rises to around 99Amps and shuts down and resets and starts this over again.
The other issue I have is that I can hear the generator change speeds when the above happens and after a couple of times the generator with go off on a faulure of Low Frequency.
Please let me know your thoughts.
Thanks Dan
Comments
14,000 Watt genset rating / 240 VAC = 58.3 amps max continuous rating
Some of the equipment will, if you program 60 amps "branch circuit" rating will only draw 80% of that:
60 Amps max rating * 0.80 = 48 amps functional draw
Which is what I would suggest you start at for a maximum draw for your genset.
Your genset will surge to 20,000 Watts (I think, just a quick looks at the specs):
20,000 Watts / 240 VAC = 83.3 Amps max
So, drawing 99 amps (@ 240 VAC on AC2 input?) does not seem right.
-Bill
If the generator is audibly struggling that would be an indication of overloading, which in turn would reduce the frequency, did you or someone else commission the system.?
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
You need to know what frequency the genset is at when it connects. Do you have a means to read gen frequency? You can read this on the combox meters screen for AC2.
The other issue with these older inverter/chargers is the stacking for multi inverter. Cables are good? Works fine without the genset?
This needs to be solved ASAP because you can damage the input relays, or one of the two or both have been damaged.
I would get one of the units (the master) working correctly, reduce charge current and test. Then add the second. As MichaelK suggests you only need 80amps or a bit more to charge. Two chargers is too much for your bank anyway.