Should I have a lower amp breaker?
Solarguy1
Registered Users Posts: 9 ✭✭
Hello,
I have these solar panels (below) which I am hooking up in series. I was sold a MNEPV20-300 breaker (20 amp) with the help from a salesperson here on the website. I am wondering if I should have a lower amp breaker since the current is 8.50 amps in series. 20 amp seems a little high to me. Should I get one instead that is closer to 12 amps? I am figuring 8.5 amps x 1.25 = 10.625 amps...
As always, Thank you!
Some one from the Northern Arizona Wind and Sun website?
Perhaps they looked up a different REC 260 watt panel.
On the back it tells you what you need;
Yes, I gave all info and that's what breaker I was sent. I am just going over everything and noticed it is a 20 amp. So 15 is max, but should I get the 12 amp since that is a little closer to the 10.625 amps target? Or, am I splitting hairs???
Yea, you should get the correctly rated breakers/fuses... Too small of fuse/breaker, you can have false trips. That is just a pain.
Too large of rating, you run an elevated risk of fire if something gets shorted...
Note that "heat" goes with the square of the Voltage or Current:- Power = Voltage*2 / R = Current^2 * R
- 15a^2 = 225 a^2
- 20a^2 = 400 a^2
The panels are rated/tested against the rated overcurrent protective device. Running outside those ratings is always a risk... And if, heaven forbid, something does "catch fire", your insurance may go over your system with a fine tooth comb to figure out a way to avoid paying out.