Trace SW4024 refuses to stay sync'd with grid AC and charge
Steve777
Registered Users Posts: 7 ✭✭
Been living with an older (circa 1999) SW4024 on a grid tied system with PVs. Just recently we were under a forced evacuation due to a nearby fire, grid AC was turned off. I made sure to turn off all non-essential loads on the PV before I left, but expected that they would still slightly overdraw the system. We were gone for 4 days. We just returned, no damage to anything. The AE system was pretty much as I expected, the sw4024 had shut itself off due to low batt (24.0v), solar during the day appears to have raised the batt voltage to 24.5v but that was still less than the cut-in voltage of 25v. No problem, just waited for the grid to go back on.
When the grid did finally come back, the inverter went into a strange cycle. Tie light is yellow. When grid is applied to AC1 the AC1 good light flashes green. If the inverter is switched off, it NEVER goes solid green indicating good AC, just keeps flashing. If the inverter is on, it flashes for 15 sec or so and then it goes solid. The bulk charge light comes on solid yellow (as expected, the batt is low). After about 10 sec of charging the bulk light goes off and the AC1 good light starts flashing again. While the inverter is on, this cycle can repeat for many hours.
I have tried turning the AC1 input off for a while (at its breaker). Does not make any diff. I have tried removing almost all the AC loads from the inverter, again no difference. FWIW, when I watch the batt voltage and current during that 10 sec interval when it is supposedly doing its bulk charge, I see absolutely no difference in voltage or current on the batts. Does not seem that bulk charging is really ever starting in spite of what the light may say.
When I monitor the grid AC with a DVM, I do not see any obvious dips or blips at all, and nothing that would sync up with the sw4024 cycling. Could be frequency or waveform variations I suppose, but unfortunately I don't have a way to measure those. I did check with some neighbors who have grid tied inverters and their equipment is not having any problems (not older trace stuff, but still).
This inverter has been rock solid for almost 20 years. It has gone through many times of the grid going down, inverting from the batts, and then coming back up and recharging the batts when the grid is back; most recently about 6 weeks ago. Although most (but not all) of those times the batts did not get drawn down to low cut-off voltage.
Right now, my next step is going to be to wait for a sunny day to get the batts up over the cut-in voltage and see if that makes any difference.
Other than that, thought I would ask here, to see if someone out there can see what might be going on from these symptoms. Anyone know what the trace checks at the beginning of a bulk charge, and what (if anything) might kick it back out of bulk and have it start rechecking the quality of the incoming AC?
Any ideas?
Thanks in advance.
Comments
-
If your inverter has an AC2 input set, have you tried that ?
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
OK, think I have found the issue, although I am still a bit puzzled.After the batt voltage was above the cut-in setting today, I did some more testing with largely the same results. However I noticed that the trace had its inverting light on but no power was present on the output circuits. Then I stumbled upon a small 35A breaker on the side of the trace near the AC wiring connections, the AC output breaker I believe. That had popped. Once I reset it, things were working normally again.Glad things are working, but it seems odd to me that the AC output breaker being open would cause issues with the inverter sync'ing with the AC input, and being able to run the DC battery charging??? Also odd that the inverter output breaker tripped error was not set (no errors were set). Good to know about this connection for the future though.
-
Those old units are tough as nails. We have so many homes here in Baja still using old trace equipment. Most of these trace inverters are 12 volt versions and no matter how much sense it makes for these people to switch to higher voltage systems they cant bring themselves to pulling a "perfectly good" inverter.
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
Categories
- All Categories
- 220 Forum & Website
- 128 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 189 Solar Information links & sources, event announcements
- 885 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 606 Discussion Forums/Café
- 300 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed