24 v inverter efficentcy
alcatel99
Registered Users Posts: 31 ✭✭
i know it depends on quality and useage but how much more efficent is a 24 v inveterr than a 12v inverter give the same amp//hr battery bank running the different voltages hope that is understandable.
Here is a nice data sheet for Victron products--Same wattage across 12/24/48 volts and from small to medium sized:
https://www.solar-electric.com/lib/wind-sun/Phoenix-Inverter-VE.Direct-250VA-1200VA-DS.pdf
According to their chart, there is around a 1% difference between 12 volt and 24/48 volt inverters (higher VDC input, slightly more efficient).
Notice the larger the Wattage Inverter, the higher the "Zero Power" (Tare losses) are.
More or less, find the smallest (Wattage) inverter that will meet your needs. Small loads on large inverters are generally less efficient (higher zero power/tare losses).
PSW/TSW inverters tend to have higher tare losses vs MSW.
Inductive/non-linear loads tend to be much less efficient on MSW inverters vs PSW. The "lost MSW energy" ends up in the induction motor / transformer / some power supplies as "waste heat" (can be damaging--Shorten the life or even kill some devices).
The bigger issue is problems sending 12 volt power (current) with low voltage drop any distance over a few feet... You need very heavy copper cable to keep the 12 volt wiring voltage drop to less than ~0.5 volts (or loads) or less than ~0.1 to 0.05 volts for charger to battery bank connections.
One example is the specs on the old Trace DR series inverters. The 12 volt DR1512 has a surge rating of 3500 watts for a minute while the otherwise identical 24 volt DR 1524 has a one minute surge rating of 4400 watts.Island cottage solar system with approximately 2300 watts of panels, 1kw facing southeast 1.3kw facing southwest. All panels in parallel for a 24 volt system. Trace DR1524 MSW inverter which has performed flawlessly since 1994. Outback Flexmax 80 MPPT charge controller four 467A-h AGM batteries. Insignia 11.5 cubic foot electric fridge 1/4hp GSW piston pump. My 32nd year.
thanks for the replies guys
Just out of curiosity, Is your forum name in any way related to Alcatel Lucent Batteries? I had a starter set of some 145 ah. Alcatel AGM's.
thanks for the replies guys no its my phone make