Over/Under Absorb

pabloesguapo
pabloesguapo Solar Expert Posts: 116 ✭✭
What happens if a battery bank's absorb time is set too low?  Or too high? 
27 Kyocera panels, 6,500w
24 CG2 6v batteries, 48v, 630Ah
Midnite Classic 150 & Classic 150 Lite in "follow me" mode
(2) Outback fx3648 inverters
Generac ecogen 6kw backup generator
Mate3s

Comments

  • mike95490
    mike95490 Solar Expert Posts: 9,583 ✭✭✭✭✭
    Too low, and the battery never fully charges and begins to sulfate and loose capacity.

    Too long, AGM :  will vent/gas and looses electrolyte that cannot be replaces
    too long flooded :  will heat up a bit, maybe flake off plate material, but generally only needs a bit extra water.
    Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||