Charge voltage for 48v bank

Options
rgk1
rgk1 Solar Expert Posts: 134 ✭✭✭
Just got 8 new Sam's club (Duracell) GC2 batteries and will be making the move to 48 volt system.  Will reprogram the Tristar MPPT 45 controller.  Just looking for recommendations for bulk/absorb/float and EQ voltages.
4-Risen 320 watt in series/parallel, 8-215ah 6 volt GC2 batteries in series, Exeltech 1100 watt/48 volt inverter, Tristar 45 MPPT controller.

Comments

  • Raj174
    Raj174 Solar Expert Posts: 795 ✭✭✭✭
    Options
    I believe this is what you're looking for if your batteries are 215 amp hour. These voltages are for 24 volt, so double for 48 a volt bank.

    https://forum.solar-electric.com/discussion/339311/duracell-branded-6v-info

    Rick
    4480W PV, MNE175DR-TR, MN Classic 150, Outback Radian GS4048A, Mate3, 51.2V 360AH nominal LiFePO4, Kohler Pro 5.2E genset.
  • rgk1
    rgk1 Solar Expert Posts: 134 ✭✭✭
    Options
    Thanks Raj174  As common as these batteries are I figured the numbers had to be somewhere but I couldn't find them.
    4-Risen 320 watt in series/parallel, 8-215ah 6 volt GC2 batteries in series, Exeltech 1100 watt/48 volt inverter, Tristar 45 MPPT controller.
  • rgk1
    rgk1 Solar Expert Posts: 134 ✭✭✭
    Options
    I did notice from this link that there is no Bulk voltage listed. It only shows a C/10 rate. Is Bulk and Absorb the same thing here?
    4-Risen 320 watt in series/parallel, 8-215ah 6 volt GC2 batteries in series, Exeltech 1100 watt/48 volt inverter, Tristar 45 MPPT controller.
  • Raj174
    Raj174 Solar Expert Posts: 795 ✭✭✭✭
    Options
    Yes, bulk really just describes the constant current charging phase. The absorb voltage setting is what the charger uses throughout the bulk charging phase. So, yep, the same.
    4480W PV, MNE175DR-TR, MN Classic 150, Outback Radian GS4048A, Mate3, 51.2V 360AH nominal LiFePO4, Kohler Pro 5.2E genset.