We have 9 315 watt panels what size breakers should I use at the combiner box.

Comments

  • Photowhit
    Photowhit Solar Expert Posts: 6,003 ✭✭✭✭✭
    Options
    Voltage differs, The panels should have a 'series fuse' rating.



    This is the size fuse or breaker needed for a single panel or a series/string of these panels. Usually 15 or 20 amps.

    If the information isn't on the back you can usually look up the information in the panels info sheet. often easiest to find by typing in you panel and brand  into google and add pdf something like '315 watt goodOldPanel pdf'