best way to switch between a MSW inverter and home AC mains
I want to use this MSW inverter as backup power for my home well pump:
https://theinverterstore.com/product/5000-watt-modified-sine-inverter-12-vdc-to-240-vac
Its manual says that the AC neutral is bonded to ground so it I assume it will not "short out" if installed with its neutral connected to ground. I've read on here that, generally, MSW inverters should NOT have their AC grounds bonded with neutral.
From the manual:
--------------
The neutral (common) conductor of the power inverter AC output circuit is connected to the chassis ground. Therefore, when the chassis is connected to ground, the neutral conductor will also be grounded.
This conforms to national electrical code requirements that separately derived AC sources (such as inverters and generators) have their neutral tied to ground in the same way that the neutral conductor from the utility line is tied to ground at the AC breaker panel.
-------------
So, it seems like I can tie together the house ground, the inverter ground, and the well pump ground... and use a DPDT switch or relay to switch the 2 legs of 240v power between mains power and inverter power. Does this seem true?
The water pump is not presently wired with a neutral, just the 2 hot legs and a ground.
I'm using it with a 12v solar MPPT controller and 100 ah battery.
Thanks for any opinions!
https://theinverterstore.com/product/5000-watt-modified-sine-inverter-12-vdc-to-240-vac
Its manual says that the AC neutral is bonded to ground so it I assume it will not "short out" if installed with its neutral connected to ground. I've read on here that, generally, MSW inverters should NOT have their AC grounds bonded with neutral.
From the manual:
--------------
The neutral (common) conductor of the power inverter AC output circuit is connected to the chassis ground. Therefore, when the chassis is connected to ground, the neutral conductor will also be grounded.
This conforms to national electrical code requirements that separately derived AC sources (such as inverters and generators) have their neutral tied to ground in the same way that the neutral conductor from the utility line is tied to ground at the AC breaker panel.
-------------
So, it seems like I can tie together the house ground, the inverter ground, and the well pump ground... and use a DPDT switch or relay to switch the 2 legs of 240v power between mains power and inverter power. Does this seem true?
The water pump is not presently wired with a neutral, just the 2 hot legs and a ground.
I'm using it with a 12v solar MPPT controller and 100 ah battery.
Thanks for any opinions!
Comments
First, a MSW inverter will cause your pump to run hot and waste about 20% more power as heat.
Second, say it's a half HP pump, that would actually consume about 1,000watts. At 12V, that's 83 amps and will need more battery and very heavy wire.
edit:
Third How often will this pump run off a battery ? how long each cycle ? Can you consider using four 6v batteries in series to get 24VDC and that takes your amps down to 40A which would be much more manageable.
Fourth. A MSW inverter will put half output voltage on one of the battery terminals, so your battery and solar panels could end up floating at 120VAC
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister ,
My 12v solar system is already in place. It's small - with 2 100 watt panels, a 10 amp MPPT controller and a Vmax 100ah battery.
I use it primarily to drive 12v internet equipment as a backup. BUT - I also have a 24amp DC charger that I could run off a generator if my solar can't keep up. That's what I think I'd end up doing for any extended use of the inverter. I don't presently have any inverter hooked into the system.
As far as the pump - how often it would run and the cycle - the cycle is about 40 seconds and I think i'd be very conservative with water and it would run maybe 5-10 times a day. Just enough for a quick shower and hand/dish washing. It's a very small cottage with 2 people. The pump draws 1000 watts at 240v as measured by my wattmeter. And I actually have a 2nd 100ah battery that I could hook to the inverter if the first one runs out and is being charged.
But the battery itself - you're saying that a 100ah capacity is too low to realistically drive the pump at all. I did ask this question to the folks at theinverterstore and their answer based on my above anticipated usage is that it "should work fine" - bad advice? Also they're marketing this inverter as a specifically good choice to drive a well pump. Their description:
----------
https://theinverterstore.com/product/5000-watt-modified-sine-inverter-12-vdc-to-240-vac/
The AIMS Power 5000 Watt inverter with 240 volts AC output is a great choice for an off grid well pump that requires 240VAC to operate. Whether for a well pump or a 240 volt motor that needs back up power, the AIMS Power 5000 Watt 240VAC inverter is a great option.
-----------
They're also specifying 4/0 awg battery cables and a 500 amp fuse for the DC. What's your opinion on that?
Also your comments on the inverter floating 120v to my solar, I think I would then disconnect the solar when I fire up the inverter so that a good tip, thanks.
I appreciate your comments and warnings - and again - this is absolutely for the occasional power outage. I could run the pump with my generator directly but when I wake up at 5 in the morning and the power's out I don't have time to drag out the gen and hook it up. I'd rather just switch on the inverter.
Thanks! Further input appreciated!
How long are your inverter power cables to the battery ?
1kw running load, is likely 5kw for starting the motor, so thats a 450A load on the batteries and you will want cables rated for at least 200A continuous, or the voltage sag will shut the inverter down. if more than a couple feet cable length, you have to go even larger. And you can bet the chassis wires inside the 5kw inverter, are nowhere near the the required gauge.
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister ,