Classic 150 won't charge
Belize1
Registered Users Posts: 19 ✭✭
Classic 150 appears to be normal but won't acknowledge the PV input. Everything in the 150 looks good but it always sits on Resting even though the PV is delivering 130 volts.
Residential Backup System Midnite Solar MN5048 Inverter/Charger 16) 235AH Crown CR235 8) Hanwha Qcell Peak Duo 350watt
Could you post picture off the display.
Copied from the link below, which was copied from else where...;
To find the "LAST Reason For Resting"
From the main status screen hold the left arrow and tap Enter. The top middle number is the "Last" RFR
Remember this is over written the next time it goes to resting
This table was stolen from a post by boB - hope to make it easier to find:
Reason For Resting:
ReasonForResting = 1 Wake state, (Vpv < PreVoc AntiClickSenstvty (MB Addr. 4236)
ReasonForResting = 2 Insane Ibatt on WakeUp state (offset changed from off state)
ReasonForResting = 3 Negative current on WakeUp state
ReasonForResting = 4 dispavgVpv < (dispavgVbatt - 10) Now -25 (RestartTimerms = 1500)
ReasonForResting = 5 Too low power and Vbatt below set point for 90 seconds
ReasonForResting = 6 FETtemperature >= 100C Hot
ReasonForResting = 7 Ground Fault
ReasonForResting = 8 Arc Fault
ReasonForResting = 9 (IbattDisplaySi < -15) (negative current) (MB 4200)
ReasonForResting = 10 (dispavgVbatt < LBDlowV) Battery less than 8 Volts
ReasonForResting = 11 Vpv >= 90% of Voc but slow. Low Light #1
ReasonForResting = 12 Vpv < 90% of Voc Low Light #2
ReasonForResting = 13 Vpv > (Voc + 10V) in PV_Uset || Solar1_OandP
ReasonForResting = 14 Vpv >= 90% of Voc but slow. Low Light #3
ReasonForResting = 15 Vpv < 90% of Voc and taking too long. Low Light #4
ReasonForResting = 16 Normally because user turned MODE OFF... Disabled
ReasonForResting = 17 Vpv > 150V (classic 150)
ReasonForResting = 18 Vpv > 200V (classic 200)
ReasonForResting = 19 Vpv > 250V (classic 250)
ReasonForResting = 22 Average Battery Voltage is too high above set point (RestartTimerms = 2 sec)
ReasonForResting = 25 Battery breaker tripped (Vbatt shot up high)
(If RFR = 25 on Wakeup, check modbus register 4200)
ReasonForResting = 26 Mode changed while running, Vabsorb raised more than
10.0 Volts or Nominal Vbatt changed by modbus command
AND MpptMode was ON when changed...
ReasonForResting = 27 bridge center == 1023 (R132 might have been stuffed old units)
ReasonForResting = 28 NOT Resting but RELAY is not engaged for some reason
ReasonForResting = 29 ON/OFF stays off because WIND GRAPH is insane
ReasonForResting = 30 PkAmpsOverLimit (will change somewhat 1-23-2013)
ReasonForResting = 31 AD1CH.IbattMinus > 900 (peak negative battery current)
ReasonForResting = 32 Aux 2 Logic input is high. Aux2Function 15 (external disable/enable)
ReasonForResting = 33 OCP in a mode other than Solar or PV-Uset (1-10-2013)
ReasonForResting = 34 AD1CH.IbattMinus > 900 Classic 150,200 newer than 1-23-2013
ReasonForResting = 35 Vbatt < 8.6 V (LOW LOW battery)
ReasonForResting = 36 Battery temperature is Greater than reg address 4161 specified
ReasonForResting = 38, is the new sleep because "other charging sources appear to be active"
ReasonForResting = 136 Battery temperature fell below MB reg. 4161 - 10 C (Classic turned back on)
ReasonForResting greater than 100... 100 + PowerOnReset, WDT, etc...
ReasonForResting = 104 Watchdog WDT reset (only at boot until first RFR)
ReasonForResting = 111 Normal Power up boot (only at boot until first RFR)
[ 100 + 1 = POR, 2 = Ext. Reset 4 = WDT 8 = Brown Out ]
http://midniteftp.com/forum/index.php?topic=2034.0
Further testing. PV tested with a meter has 130 volts when disconnected from the 150. When the PV cable is connected to the 150 terminal, the cable now reads zero..Residential Backup System Midnite Solar MN5048 Inverter/Charger 16) 235AH Crown CR235 8) Hanwha Qcell Peak Duo 350watt
Sounds odd... Typical issues are a confusion between what is + and - from each panel (the MC4 connections can be "reversed wired" between brands, etc.).
The other would be is that there is an "almost open" electrical connection somewhere (bad crimp, pulled crimp, bad spotweld/connection in panel J-Box, etc.).
You might need to pull every connection, check voltage and current at each point, then reconnect.
I don't know about the Midnite controllers, but some devices will put a "crowbar" across an input (or output) connection. If something goes wrong (+/- reversed, over voltage, etc.), the "crowbar" shorts the connection.
So, double check that +/- 130 Volts is the proper polarity at the Vpanel input for the controller (a possibility, not sure that this would happen here).
this installation has been working for 2 years and only recently went into resting state where it seems to cancel (or ground out) the incoming PV voltage. Possibly following a lightening strike? No visible damage anywhere, just this constant restingResidential Backup System Midnite Solar MN5048 Inverter/Charger 16) 235AH Crown CR235 8) Hanwha Qcell Peak Duo 350watt
Water in a connection somewhere?
Did you check what code the Classic is giving you?
Photowhit gave the way to find the "Reason For Resting". What is the RFR number?
If you open the PV in breaker to the Classic, what is the Vin shown on the display?
Thanks, Vic
Usually when you see zero volts at the input only when the PV array is connected to the input it means one of two things....
Either the polarity of the PV is backwards, but your system has been working so that cannot be it.
OR, the Classic is broken. Shorted input. Bad FETs. Usually when you disconnect the PV from the PV input, you would see some arcing if the sun is out.
Call MidNite Solar technical service. 360-403-7207
real easy to troubleshoot this.insert ammeter in pv input right at controller.i usually use the + lead.remember it may be live if you forgot to pull the disconnect first!reading low or no current?likely bad connection,panel,ect.reading near expected isc of the array?problem is in the controller input.