Sizing a Solar System
flavioseferi
Registered Users Posts: 2 ✭
hello evrybody !
Im doing an intership in a solar energy company in europe and im facing a problem right know.
We have a 11.2 Kw system where we are going to use 40 panels (Peimar 280W) and a ABB 12.5 KW solar inverter.
My question is how many strings and how many panels for each sting should i use?
Trying to seize the system in PVSOL i find it impossible becouse the PVSOL system told me that the inverter is incompatible.
I'll preciate you help guys.
Assuming the inverter is a dual mppt high voltage type, and the panels are ~30vmp, my guess would be maybe 2 strings (one on each mppt) for about 20 x 30 = 600v. Voc would need to be checked to confirm it's under the max at record low temp for the location.
Are there panel optimizers involved?Off-grid.
If you post the panel specs ( Voc, Vmp, Imp ) and the inverter specs ( Turn on V___ MPPT volt range __ to ___V and Max input Volt___)it'd be easier for us to divine what might workPowerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
Hello evrybody thank you for your response.
Im posting the panels and inverters specs :
Panels specs :Voc=37.3V ,Vmp=31.2V,Imp=8.98A
Inverter specs : Vstart =360V ,Absolute max DC input Voltage=900V,(Vdcmin....Vdcmax=250....850V)
Im attaching the datasheet of the products below to be more precise.
Thank u Guys i really appreciate you help
18 panels in series is the most I'd run, unless you are in a place it gets really cold, then 16 or 17 in series,12 panels in series is the minimum you can use,having 20 panels in series would look nice on paper, but a cool morning stands a good chance of taking your inverter out from high voltage. 20 x 37.3 = 746v at 45C
- 230 Forum & Website