Help with breakers
toryc19
toryc19 Registered Users Posts: 2
Hi, I need help, I have had many electricians that have no idea how to help me with installing breakers for my system,  Its for a small cabin, I have a 5kw inverter charge controller all In one.  It states it will use 200amps between batteries and 60 amp between pv and inverter.  I have two 330 watt solar panels and two 200 amp batteries ( i know I need more but if I can just get lights on right now it would be great!)  I someone could give me a diagram on how to do this and what breakers, how many and disconnect, combiner boxes etc so my electrician can do this for me... thankyou!!
  • Estragon
    Need to know the nominal voltage of the battery bank.
    5kw inverter and 660w of pv suggests to me there may be some design issues, as you likely already know.
    Not a lot of electricians know much about the DC side of things.
  • icarus
    5kw inverter with only 200 ah of batteries?  Ugh!  Brand names would be helpful, including voltage specs A 5kw inverter from 12 vdc would require a ~400 amp breaker/fuse. From 24 vdc ~200 amps.  The inverter loses are likely to be a bigger load on the battery than the lights you are trying to power!
    Bottom line...off grid systems need to be balanced between loads, battery capacity and charging regimen.  Using such a large inverter is going to be problematic.  For 600 watts of PV, powering a few lights, consider charging out the hardware for a Morningstar sursine 300 inverter and a Midnight Kid charge controller.  We have run our entire house on such a set up for 15 years, using 450 ah of 12 volt batteries. (4 6 volt T105s).
  • toryc19
    ok, I have 2 renogy 200ah batteries totaling 400, I can get some more....of course I didn't know what I was doing when I ordered it...its a VOLTACON, i also have two more solar panels of the same 330 watts, if i have to get a different set up i will, just hoping i don't have to.  And i would like to power more than lights, like the whole cabin. here are the specs
    This may help.  or not. (my system, which has been added on to since drawn)
    Using pre-wired DC epanel from Midnight is a big help, saves "reinventing the wheel".
    Since this, it's been upgraded with a 2nd PV array 2Kw and Midnight Classic 200 charge controller, which also wired up through provisions (breaker knockouts) in the epanel. Genset is a flywheel crank, 3kw diesel.
  • littleharbor2
    littleharbor2 Solar Expert Posts: 2,172 ✭✭✭✭✭
    Boy, ain't that the truth.
  • Estragon
    5kw inverter is really pushing it on a 24v system.  Whether it's better to start over or make do adding to what you have comes down to what else you want to run in the cabin besides lights.  A spreadsheet listing each load, how much power it takes, and how long it's used daily would be helpful.
    5kw is ~200a, requiring ~3/0 or 4/0 (about thumb size) wire from the inverter to batteries and 200a DC rated breaker.  The spec shows a "DC disconnector" (breaker?) rated at 100a with 00 (2/0) connection.  Maybe the 5kw is a surge (eg 5 sec) rating, with 2.5 kw continuous rating?
    Wiring 2 x 12v batteries in series (using the same thick wire for interconnects) gives you 200ah at 24v or ~4800 watt-hours, of which you shouldn't use more than 50% in regular use.
    Charge controller output is listed as 80a.  It isn't clear if there's a separate connection to the batteries, or it shares the battery connection with the inverter via an internal buss.
  • icarus
    How about you give us an idea of your load(s) and we can see if any of this makes sense?  My guess is that this is a “ready, fire, aim” system that is likely to perform very poorly...sorry to say.  All off grid hardware choices stem from the loads.