wire size
ws9876
Solar Expert Posts: 453 ✭✭✭
Would you use 10/3 Romex solid to join a 2500 watt inverter 120v to a mains panel 65 ft away?
Romex or NMD 90 has restrictions for its useage, particularly with regards to mechanical protection, if running a single 120V circuit a 2 conductor cable is all that's required Note. The third uninsulated ground in a 10/2 is not counted as a conductor.
For 65 feet with 10 AWG the voltage drop would be acceptable at 2500W load at 2.6% voltage drop https://www.calculator.net/voltage-drop-calculator.html?material=copper&wiresize=3.277&voltage=120&phase=ac&noofconductor=1&distance=65&distanceunit=feet&eres=20&x=31&y=261500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
would you use 10/2 romex solid from solar panels 50 ft to charge controller?? or would you use 2 pieces of 10 awg copper stranded?
Stranded or solid does not really matter electrically or for straight runs... Stranded will be much easier to bend and get around corners.
When you get to larger AWG wiring (like 8 AWG or larger), it is generally easier to work with stranded.
-Bill "I am not an electrician" B.Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
I'd be inclined to use stranded if/where subject to vibration or other movement (wind etc). Stranded can be tough to get properly into a tight connector though.Off-grid.
- 654 Solar Water Pumping