Outage backup (120 and 240) in grid-tie system
Tricksailing
Registered Users Posts: 25 ✭✭
I'm installing a grid-tie system in Baja Sur, Mexico and would like to include an emergency back-up for the not-so rare power outages triggered by storms. In some cases outages have lasted for days.
The most important appliances are refrigerator/freezers but it would also be nice to cool at least 1 room with AC and keep the water pressure boost pump running, both of which run on 240v.
I'm considering a Sunny Boy (7.7) inverter to take advantage of the Secure Power Supply (SPS) with a generator to take care of nighttime consumption. Are there other options I should consider?
A problem with the Sunny Boy is that the SPS is only 2 kW which would be pushing things to run a 1.5 ton AC along with a couple of refrigerators. The other problem is that the SPS is only 120v so would need a step-up for 240. It doesn't look like SPSs from a pair of smaller Sunny Boys can be synced for more power/volts so I suspect a step-up transformer would be the solution for 240v.
It would be nice to have the system hooked into the house wiring (with appropriate interlocks to keep power off the grid). I'm envisioning a 120/240v center tap transformer (or a pair of 120/120 transformers) hooked into the SPS with a grounded center tap to mimic the house supply. Is this possible, or would issues of inbalanced loads on the 120 lines create too many problems?
As I noted above, I'm still planning this and am open to alternative suggestions.
The most important appliances are refrigerator/freezers but it would also be nice to cool at least 1 room with AC and keep the water pressure boost pump running, both of which run on 240v.
I'm considering a Sunny Boy (7.7) inverter to take advantage of the Secure Power Supply (SPS) with a generator to take care of nighttime consumption. Are there other options I should consider?
A problem with the Sunny Boy is that the SPS is only 2 kW which would be pushing things to run a 1.5 ton AC along with a couple of refrigerators. The other problem is that the SPS is only 120v so would need a step-up for 240. It doesn't look like SPSs from a pair of smaller Sunny Boys can be synced for more power/volts so I suspect a step-up transformer would be the solution for 240v.
It would be nice to have the system hooked into the house wiring (with appropriate interlocks to keep power off the grid). I'm envisioning a 120/240v center tap transformer (or a pair of 120/120 transformers) hooked into the SPS with a grounded center tap to mimic the house supply. Is this possible, or would issues of inbalanced loads on the 120 lines create too many problems?
As I noted above, I'm still planning this and am open to alternative suggestions.
5kW grid-tied SMA + 2kW grid-tied SMA (total 4kW emergency daytime power) + 2kW genset, 500W off-grid marine system. Baja Sur.
Tagged:
Comments
-
Tricksailing said:I'm installing a grid-tie system in Baja Sur, Mexico and would like to include an emergency back-up for the not-so rare power outages triggered by storms. In some cases outages have lasted for days.
The most important appliances are refrigerator/freezers but it would also be nice to cool at least 1 room with AC and keep the water pressure boost pump running, both of which run on 240v.
I'm considering a Sunny Boy (7.7) inverter to take advantage of the Secure Power Supply (SPS) with a generator to take care of nighttime consumption. Are there other options I should consider?
A problem with the Sunny Boy is that the SPS is only 2 kW which would be pushing things to run a 1.5 ton AC along with a couple of refrigerators. The other problem is that the SPS is only 120v so would need a step-up for 240. It doesn't look like SPSs from a pair of smaller Sunny Boys can be synced for more power/volts so I suspect a step-up transformer would be the solution for 240v.
It would be nice to have the system hooked into the house wiring (with appropriate interlocks to keep power off the grid). I'm envisioning a 120/240v center tap transformer (or a pair of 120/120 transformers) hooked into the SPS with a grounded center tap to mimic the house supply. Is this possible, or would issues of inbalanced loads on the 120 lines create too many problems?
As I noted above, I'm still planning this and am open to alternative suggestions.4480W PV, MNE175DR-TR, MN Classic 150, Outback Radian GS4048A, Mate3, 51.2V 360AH nominal LiFePO4, Kohler Pro 5.2E genset. -
I agree with Rick. The transformer will be useless with the 2KW 120vac source, for most loads, and only when the sun is out.
Your choices are a genset for back-up or a Hybrid like the Radian or Schneider XW+/Pro
"we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 622 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed