Grounding Question
Hi.
Re: Magnum Battery Inverter MS4448 PAE. 4400W, 48 VDC, 120/240 VAC 60Hz
We luve off grid in an usland here in Belize, C.A. We have no grud VAC or generation hooked into our system. It will run off 48V battery bank powered by solar panels.
My question is...on our inverter connections I see ground IN, ground OUT and Equipment ground. Do I need to ryn the grounds IN & OUT to my house panel? (30 feet away )
In the house I have a main Circuit Breaker Load Center (Square D, QO by Schneider Electric )
Thanks for any help, Mike
Comments
-
IMHO, you should run from the inverter ground OUT to the AC panel ground. With no secondary AC (grid/generator/etc) the inverter ground IN would be unused (as would AC live and neutral INs).
Check the inverter manual, but I think there should be a neutral-ground bond made in the AC panel.
Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Thanks why do I bond the neutral to the ground ? Won't this make the ground carry current all the time?
-
Generally, you want to "bond" the Neutral to Green Wire/Safety ground in one location... For North American homes, that is typically inside the main breaker/fuse panel (you will see both a green wire ground bus, and a white wire neutral bus--And somehow, they will be attached together inside the panel).
Note, this is not really true outside the home.. For example, you have a pole mount 120/240 VAC Split Phase transformer on the pole. The neutral is grounded (typically) at the base of the pole. Also, this transformer serves ~5 homes on your block, and each home has a ground to neutral bond too). In the grand scheme of things, this is very good for lightning control (lightning takes the shortest path to ground--It does not like to follow electrical wiring more than a few 10's of feet). And the resistance from ground to earth only carries, perhaps, 5-10 amps or so worst case (120 VAC / 25 Ohm worst case grounding=4.8 amps)--So, the "AC ground current" does not really do much when you have 5 volts drop from pole to house (5 volts / 25 Ohms=0.2 amps).
Inside your home, when you have "single point" ground to neutral bonding, there is no connection for parallel current flow on both Neutral and Ground wire.
However, if you tied white to green both in the main panel, and (for example) at an outlet. Then the current flow will be divided between white and green because of this. And we do not want this (don't want current flow through green wire unless it is, for example, a short circuit from Hot to Ground--To trip the breaker). There are further details why multi-point grounding of a home's neutral system with the safety ground is not good/safe... We can discuss more if you are interested.
Grounding is one of the most complex questions we talk about here... There is a good reason why the best idea is to follow code--This helps reduce "inadvertent" problems (things people and equipment don't "expect").
Things do get complicated when you talk about gensets and RV installations with multiple power sources (utility, genset, AC Inverter).
For example, in my (limited) experience, more or less, smaller (3,000 Watts or less?) gensets and AC inverters do not ground bond neutral and ground. And most will ground bond in the genset/inverter if over ~3,000 Watt output. So, this gets complicated when you are powering your home with utility power, a backup genset, AC inverter... The typical answer for your home, is to make sure that the white/green wire bond is "lifted" in the (larger) gensets and AC inverters.
For RVs, because of the complexity (for example, at the RV park, their neutral/green wire ground is somewhere back on their AC panels). Using a transfer switch with an extra lead to ground bond when the genset or AC inverter are supplying power, and "not bond" when utilty power is supplied.
And even more complexity, (generally) you should only ground bond a PSW/TSW (pure/true sine wave) AC inverter (Hot and Neutral are "floating"/isolated by a transformer). For MSW (modified square/sine wave) do not neutral/ground bond the output of AC inverters because the AC output is not isolated (connects back to the battery +/- bus, no transformer isolation).
That is some of the details behind why the answer depends on your system's details. Short answer is neutral+ground bonding does not create a parallel current path with single point bonding.
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
But if Ur ground enters earth at 2 points... Even if those 2 points are also bonded to each other, AND even if all Ur neutrals are only bonded at the main panel and there (and there only) also bonded to ground, that is bad?
REC TwinPeak 2 285W 3S-3P 2.6kW-STC / 1.9kW-NMOT Array / MN Solar Classic 150 / 2017 Conext SW 4024 Inverter latest firmware / OB PSX-240 Autotransfomer for load balancing / Trojan L16H-AC 435Ah bank 4S connected to Inverter with 7' of 4/0 cable / 24 volt system / Grid-Assist or Backup Solar Generator System Powering 3200Whs Daily / System went Online Oct 2017 / System, Pics and Discussion -
If I follow you correctly, sounds find.
You can have multiple ground rods... Either (or both) for better lightning grounding or if you have sandy/dry/rocky soil that has poor conductivity. I suggest that running a 6 AWG between ground rods improves "safety grounding" for AC voltages and better lightning control.
"Earth Grounding" for your AC power does not really make things electrically safer (120/240 VAC). Tying Neutral to grounding and 'big metal" (water pipes, gas pipes, electrical panels, etc.) is what makes things safer. This provided a return path (from "grounded metal" back to the ground+neutral bond) so that a circuit breaker can be tripped.
Earth Grounds are generally for lightning protection (get lightning energy away from house). A short circuit from 120 VAC "Hot" only will drive ~5-10 amps into the earth--Not enough to trip a breaker.
Other grounding issues that "need earth grounding" such as making some fluorescent tube fixtures start easier, spark ignition on stoves for flame detect, and cathodic pipe/ironwork protection ("charge" the pipes so they do not rust, phone systems so they do not have their wires corrode when they get wet)...
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
just a note - Gas lines/pipes are not generally allowed to be tied into the ground system. They are often tied into a cathodic protection system to prevent corrosion
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
In the USA... In general (I am not a code expert) there is a galvanic isolation (fancy name for "insulated pipe joint" joint out at/near the gas meter (line in ground is part of utility's cathodic protection system. In the house, the gas lines were "floating").
Today, our local code requires that the gas line and hot water line be tied (grounded) to the cold water pipe and ground rod (add ground rod if not present in old / original structure).
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed