Hello there, i have my XW+ installed, everything is working great, Since I have the grid line connected to the inverter, I want to set up the Grid Support, no selling, only to allow the batteries to charge if during the night they get to 50%, could anyone please explain a bit how to do this, I have read the Owners Manual but I don't quite get the instructions there.
Tagged:
Comments
-
Your dealer ought to be able to help with reading the manual. Before you go adjusting things, you really need a good grasp on electrical terms and calculations.
Many of the settings interact with others, setting the battery size/amp hours is one that is criticalPowerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
As Mike said there are a lot of interlinked variables but here are a few settings to play with.
Grid Support enabled
under Advanced options
Grid support V try 48.4
sell disabled
I prefer to leave the charger disabled. A hard load that dips the battery voltage for more than a few seconds can activate the charger when the batteries are still a bit above your desired 50%. But if you want to leave the charger enabled I'd start with Battery recharge V at 48.2v and go from there.
Do not totally rely on your SCP or Combox battery meter. If you've got LA batteries use the SG readings regularly. good video If you run LA batteries https://www.bing.com/videos/search?q=rolls+schneider+battery+video&view=detail&mid=AF89235D2A45973D0423AF89235D2A45973D0423&FORM=VIRE
Conext XW6848 with PDP, SCP, 80/600 controller, 60/150 controller and Conext battery monitor
21 SW280 panels on Schletter ground mount
48v Rolls 6CS 27P
-
I have already set up battery Battery type = AGM and Battery bank amp which is 440ah, the LBCO = 43.4 For this number I contacted the batteries manufacturer and they stated that a bank of 48v, 50% DOD is 43.44VDC, everything is set, I have grid support enable, when I get home I will look at the rest of the options I will not turn on AC breaker until I have a better config parameters.
-
43.4v for 48v bank sounds like a lot lower than 50% SOC. My chart shows that to be a dead battery.
With your LBCO set at roughly 50% SOC and a desire for grid charging to enable at roughly the same point I'd make sure your LBCO delay is fairly long, like the 300 second max.
I set my LBCO at 47.2, about 30% SOC. Long power outages are common here, often we don't notice that the grid has been down for over a day. If the neighbors don't have power we often don't notice because the neighbors are too far away to hear a generator and nobody panics because power outages are common. The well pump may run dipping battery voltage so I went with the long 300 second delay.
May I suggest that instead of having the charger automatically cutting on you instead enable grid support. The inverter will pull about 80 watts constantly but with grid support voltage set at about 49.4v your inverter will automatically increase the use of grid voltage to supplement the battery power until it goes almost totally to grid power with very little drain on the battery when the battery gets below the set voltage. 49.4v works out to about a 70% SOC battery before the grid fully steps in and handles 98% of the load.
The roughly 100 watts is about 2.5 kwhs/day so about 25 cents a day worth of grid power used each day that the batteries stay above the set voltage.
By enabling the charger manually if you know the next day will be sunny you don't need to charge the batteries. It won't really hurt your batteries to let them sit a day at 70% waiting for the next sunny day. Your grid support will keep the house powered.
Conext XW6848 with PDP, SCP, 80/600 controller, 60/150 controller and Conext battery monitor
21 SW280 panels on Schletter ground mount
48v Rolls 6CS 27P
-
WaterWheel said:43.4v for 48v bank sounds like a lot lower than 50% SOC. My chart shows that to be a dead battery.
With your LBCO set at roughly 50% SOC and a desire for grid charging to enable at roughly the same point I'd make sure your LBCO delay is fairly long, like the 300 second max.
I set my LBCO at 47.2, about 30% SOC. Long power outages are common here, often we don't notice that the grid has been down for over a day. If the neighbors don't have power we often don't notice because the neighbors are too far away to hear a generator and nobody panics because power outages are common. The well pump may run dipping battery voltage so I went with the long 300 second delay.
May I suggest that instead of having the charger automatically cutting on you instead enable grid support. The inverter will pull about 80 watts constantly but with grid support voltage set at about 49.4v your inverter will automatically increase the use of grid voltage to supplement the battery power until it goes almost totally to grid power with very little drain on the battery when the battery gets below the set voltage. 49.4v works out to about a 70% SOC battery before the grid fully steps in and handles 98% of the load.
The roughly 100 watts is about 2.5 kwhs/day so about 25 cents a day worth of grid power used each day that the batteries stay above the set voltage.
By enabling the charger manually if you know the next day will be sunny you don't need to charge the batteries. It won't really hurt your batteries to let them sit a day at 70% waiting for the next sunny day. Your grid support will keep the house powered. -
@WaterWheel may you send me the 48v SOC Chart?
-
Conext XW6848 with PDP, SCP, 80/600 controller, 60/150 controller and Conext battery monitor
21 SW280 panels on Schletter ground mount
48v Rolls 6CS 27P
-
WaterWheel said:43.4v for 48v bank sounds like a lot lower than 50% SOC. My chart shows that to be a dead battery.
With your LBCO set at roughly 50% SOC and a desire for grid charging to enable at roughly the same point I'd make sure your LBCO delay is fairly long, like the 300 second max.
I set my LBCO at 47.2, about 30% SOC. Long power outages are common here, often we don't notice that the grid has been down for over a day. If the neighbors don't have power we often don't notice because the neighbors are too far away to hear a generator and nobody panics because power outages are common. The well pump may run dipping battery voltage so I went with the long 300 second delay.
May I suggest that instead of having the charger automatically cutting on you instead enable grid support. The inverter will pull about 80 watts constantly but with grid support voltage set at about 49.4v your inverter will automatically increase the use of grid voltage to supplement the battery power until it goes almost totally to grid power with very little drain on the battery when the battery gets below the set voltage. 49.4v works out to about a 70% SOC battery before the grid fully steps in and handles 98% of the load.
The roughly 100 watts is about 2.5 kwhs/day so about 25 cents a day worth of grid power used each day that the batteries stay above the set voltage.
By enabling the charger manually if you know the next day will be sunny you don't need to charge the batteries. It won't really hurt your batteries to let them sit a day at 70% waiting for the next sunny day. Your grid support will keep the house powered. -
We've got at least 2 other people from Puerto Rico on this forum but I can't remember their names. But if you can track them down perhaps they can help you with battery selection when your batteries get old.
Conext XW6848 with PDP, SCP, 80/600 controller, 60/150 controller and Conext battery monitor
21 SW280 panels on Schletter ground mount
48v Rolls 6CS 27P
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 190 Solar Information links & sources, event announcements
- 886 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed