Hterron: Fuse from Charge Controller to Battery Bank
System
Posts: 93 admin
This discussion was created from comments split from: fuse from charge controller to batteries.
Comments
-
Hi, Í have 2x250 watt panels in parallel with 60 amp mttp charge controller.. 10awg wire from panels to controller. what size fuse do I need to connect to charge controller to batteries ? I have 230 amp battery .
-
What voltage battery bank?
How much power (Watts) or DC Amps do you wish to draw (average worst case, peak surge)?
How long of wire run from array to charge controller, and how long of wire run from controller to battery bank?
Do you plan on larger array and or battery back in the future?
BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
In addition to Bill's questions, what wire size and fuse/breaker size is recommended by the charge controller maker for the battery connection, and what size wire do you expect to install. The fuse/breaker should be sized to protect the lesser of the controller or wire ampacity IMHO, both of which should be well in excess of normal operating currents.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
What voltage battery bank? Is a 12v
How much power (Watts) or DC Amps do you wish to draw (average worst case, peak surge)?
Around 1000 watts
How long of wire run from array to charge controller, and how long of wire run from controller to battery bank?
From array is about 10 feet. From controller to battery 4 feet
Do you plan on larger array and or battery back in the future? Yes. It will be good. -
I using size 10 cable
-
Array to CC #10 is good max fuse "OCP" 20A
CC to battery I would use #8 OCP 50A
Just my thoughts.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
Considering a 1000w inverter, @ nominal12v, could draw sustained 90-100a and surge higher, 8ga and 50a may mean having a lot of spare fuses on hand?Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Estragon said:Considering a 1000w inverter, @ nominal12v, could draw sustained 90-100a and surge higher, 8ga and 50a may mean having a lot of spare fuses on hand?1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
Yup, just having it now, and really enjoying it. After a run of 30+° weather, woke to a misty 9°C and an email with the winter storage agreement for the boat. Ugh.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
I have a 2000 watt inverter but I spec to use around 1000 watts
-
Is for a refrigerator 2 fan and 6 led light
-
Heterron,
I am going to split this into your own thread... Keeps Q&A a bit easier (does not hijack the original poster).... So don't be surprised if you have to look for this moved thread later in the day.
-Bill "moderator" B.Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Sorry for that BB. I had the same situation.
-
Not a problem Hterron,
Sometimes discussions get a bit confused if there is a lot of Q&A between people. Having your own thread usually keeps things addressing just your issues.
Regarding the wiring... Two issues, the maximum current you plan on running, and the voltage drop. If, you plan on a maximum array of 500 Watts, then:- 500 Watts * 1/12 volts * 1.25 NEC derating for continuous current = 52 Amps minimum Branch Circuit+Breaker
- 60 amps * 1/0.77 panel+controller deratings * 14.5 charging voltage = ~1,130 Watt array "cost effective" maximum
https://www.calculator.net/voltage-drop-calculator.html?material=copper&wiresize=0.8152&voltage=14.5&phase=dc&noofconductor=1&distance=4&distanceunit=feet&eres=57&x=46&y=17
4 feet of # 4 AWG cable gives you:
Voltage drop: 0.11
Voltage drop percentage: 0.78%
Voltage at the end: 14.39
And you may find, that you have to trim some strands off to get #4 AWG cable to fit.
From the NEC wire chart (summary, fairly conservative), 52 amp rating would need #8 wire with high(er) temperature insulation, or #4 with medium temperature insulation if you want to go for 80 Amp current rating:
https://lugsdirect.com/WireCurrentAmpacitiesNEC-Table-301-16.htm
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Thanks
-
You are very welcome Hterron...
And to cover all bases, you could shorten the wiring from the charge controller to the battery bank to ~2 feet, and have 1/2 the voltage drop (bit better voltage control for charging battery bank).
Take care,
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed