alternative method for connecting the AC out Terminals on my inverter
Nabiru3
Registered Users Posts: 13 ✭✭
Hey everyone I have a question about connecting the AC out Terminals on my inverter.
I have 24v/1500w off grid inverter with only AC out terminals in the back and I want to connect that to a regular AC outlet(electrical outlet). I have disassembled the AC outlet and found 3 inlets(L,N, ground) . now, on my inverter the 3 terminals are marked (Line out, Neutral, Earth), if logic didn't fail me those should be connected as (L = Line out, N = Neutral, ground = Earth(not really necessary for the flow of electricity but provides protection)). and as I turn the inverter the power should run to the electrical outlet and provides electricity just like usual.
my question is, though it is common sense to connect the AC out terminals in the inverter directly to an AC distribution panel, I am curious what will happen if I just connect them to a regular outlet (just like i described above). and if I did so with/without AC breakers what consequences can I expect.
this question and example are of Explanatory reasons only and not for actual real life application, thus I didn't provide concrete information about the tools and equipments used.
Thank you in advance.
I have 24v/1500w off grid inverter with only AC out terminals in the back and I want to connect that to a regular AC outlet(electrical outlet). I have disassembled the AC outlet and found 3 inlets(L,N, ground) . now, on my inverter the 3 terminals are marked (Line out, Neutral, Earth), if logic didn't fail me those should be connected as (L = Line out, N = Neutral, ground = Earth(not really necessary for the flow of electricity but provides protection)). and as I turn the inverter the power should run to the electrical outlet and provides electricity just like usual.
my question is, though it is common sense to connect the AC out terminals in the inverter directly to an AC distribution panel, I am curious what will happen if I just connect them to a regular outlet (just like i described above). and if I did so with/without AC breakers what consequences can I expect.
this question and example are of Explanatory reasons only and not for actual real life application, thus I didn't provide concrete information about the tools and equipments used.
Thank you in advance.
Tagged:
Comments
-
Check the manual when you peg down the "real life" inverter.
Might also check the UL rating, I suspect most UL 458 (for mobile use) will have some internal protection and UL 1741(home use) less likely. But don't know.
Easier to be safe than sorry.
Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
You may want to check the manual for info about DC grounding, wire size, overcurrent protection, and AC neutral/ground bonding in addition to breaker info. As Photowhit said, some inverters are designed to be used as you propose (wired to AC panel), and others to supply portable loads. Bad things can happen using the wrong one for the installation type.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Details do matter... Where are you at (Yemen?) and what AC voltage are you working with (in North America, usually 120 VAC. In other countries, many times 230 VAC or so).
In general, 1,500 Watts does not supply enough current to be an issue for most outlets/power systems:- 1,500 Watts / 120 VAC = 12.3 Amps
- 1,500 Watts / 230 VAC = 6.5 amps
If yo have a larger inverter, or use smaller than (typical) AC wiring, then the fusing/breakers you would use would be sized to the rated current of the wiring...
In the US, that would be 14 AWG wire for 15 amp nominal current. In UK, they use 13 amp fuses for their typical AC wiring.
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset - 1,500 Watts / 120 VAC = 12.3 Amps
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 622 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed