Hello all. Here's what I have. 6 panels 320w each 24v. I have a Midnite classic 200 with 2 banks of four t105 batteries 24v each leading into a 3000w inverter.
I've went off the spec sheet for the t105 and for some reason it just doesn't seem right.
Can someone tell me what the Eq, Absorb, Float should be for this set-up? What other settings should I be looking at? Do I need to equalize the batteries? Is there a book for dummies that has this information?
I've went off the spec sheet for the t105 and for some reason it just doesn't seem right.
Can someone tell me what the Eq, Absorb, Float should be for this set-up? What other settings should I be looking at? Do I need to equalize the batteries? Is there a book for dummies that has this information?
Comments
-
The numbers on the spec sheet I found are; bulk 29.6, absorb 28.2-29.4, float 27, and EQ/finish 32.4. All should be set to temp compensated in the classic.
The "finish" charge is a sort of mini-EQ which doesn't apply with the classic. I would set absorb to the high-ish end of the range, say 29v initially, and absorb time to 3-4 hours. If you have a whiz-bang jr (you really should), set end amps to ~1% of capacity, so 450ah x .1 = 4.5a (IIRC it's whole numbers, so either 4 or 5). Check on the batteries towards the end of absorb. There should be some gentle bubbling. If no bubbling, Vabs should be increased a bit. If lots of bubbling, decreased a bit. Also check specific gravity regularly after absorb (to let the bubbling subside) often at first to make sure the settings are getting the bank fully charged. Sometimes it takes a bit of tweaking to get voltages dialled in for your specific situation.
Trojans do have higher voltage charging specs than some others, but I'd start with recommended values and adjust as needed from there.
Also, the EQ voltage gets pretty high when temp compensated on a cool-cold bank, and can hit high limit for some inverters, etc., but yes, you need to EQ. I do mine, along with routine SG checks, roughly once/month.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Thank you that is very helpful
Categories
- All Categories
- 220 Forum & Website
- 128 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed