Equalization
woodyindc
Registered Users Posts: 1 ✭
I have a Magnum 1000 sinewave and eight 6 volt Trojan batteries. How do I equalize if I don't have a switch on the inverter
Your charge controller should have the EQ function, not the inverter. Use the inverters internal charger (if it has one) to bulk the batteries in the morning, and let solar take over for Absorb and then EQ ?Does your inveter have a charger in it ? Or use your generator and charger to bulk the batteries in the AMPowerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
Do you have or have the option to have a Magnum Remote Control Panel. I would guess you need one to fine tune the inverter settings.woodyindc said:I have a Magnum 1000 sinewave and eight 6 volt Trojan batteries. How do I equalize if I don't have a switch on the inverter
Remove the fuse or turn off the circuit breaker. You do have some form melt down protection ?
thomOff grid since 1984. 430w of panel, 300w suresine , 4 gc batteries 12v system, Rogue mpt3024 charge controller , air breeze windmill, Mikita 2400w generator . Added 2@ 100w panel with a midnight brat
- 234 Forum & Website
