best approach to string 12 2 volts agm batteries
DarkstormNH
Registered Users Posts: 48 ✭✭
Good folks
i have 12 2 volts batteries, should i string one 24 volts or 2 parallel string at 6*2=12 volts than parallel for 24 volts
feedback suggestions will be appreciated
Parallel 2x12v strings will give you a higher capacity 12v bank. If you need 24v with 12x2v cells, it has to be a single series string.Off-grid.
What are your needs? 12 volt or 24 volt. The 12 volt and 24 volt configurations store exactly the same amount of energy.
12 volt, more off the self small stuff to run. 24 volt, less voltage drop, smaller cables, more efficient use of charge controller (2x more solar panels at 24 volt battery bank).
12 volt bank needs heavier cables, has more issues with voltage drop in cables.
PS, what is the AH of the cells?
are the batteries sealed or flooded ? Series is the better configuration, if you require 12V, there can be imbalance issues between strings not sharing equally, diagonal wiring can ameliorate some of that issue.Sealed batteries have more issues when in parallel, because of their low internal resistance
BB. said:What are your needs? 12 volt or 24 volt. The 12 volt and 24 volt configurations store exactly the same amount of energy.
PS, what is the AH of the cells? -
Then there is no choice. With 12x2v cells, you will have a single series string of ~700ah @ 24v. There is no parallel option.Off-grid.
Estragon said:Then there is no choice. With 12x2v cells, you will have a single series string of ~700ah @ 24v. There is no parallel option.
You can parallel for 12 volts @ 1,400 AH. And that is 140 amps for a 10% rate of charge.
A lot of current, heavy cabling, and 2x solar charge controllers.
Of course, it does depend on your needs.