Setup camper van
Solar panel 2x 36V, 20A parallel 1440W measured by the meter.
Plan connect with:
Controller 36V 60A. 20A reserve for future solar panel.
Deep cycle marine battery 2x or 3x 12V 400A series
Inverter 24V 2000W continuous, 3000W peak
Will system work and supply maximum efficiency of output power?
In desert like area of California.Use for continuous operation of 200W compact frig, 400W computer, 15W misc. and alternative running of 400W air conditioner or 700W microwave [2.8kw peak] or 1000W tools.
Please QC and correct me if I miscalculate anything. I never used or did this before. Unsure 24V or 36V controller? Unsure 38V read solar is regarded as 24V or 36V? Many thanks.
Comments
-
You need to start with loads, with limited real estate on a mobile application, the loads would have to be kept to a bare minimum, a refrigerator alone is a major load, forget air conditioning, tough in a desert I know, but one has to be realistic, 400w for a computer is extremely high, consider a tablet or laptop at very least, microwaves although a large load it is for short durations so not really huge consumers.
Once the loads are narrowed down, then the design can begin, to answer briefly the question of voltage, 36V is not something common, you would either choose 12, 24 or 48V as a nominal voltage, the choice of which is largely dependant on loads, hense loads first, battery next then array. Hope you haven't bought any hardware yet, because it's extremely difficult to work backwards. For now forget the hardware and concentrate on establishing loads, with a set figure, the process can begin. To establish loads watts alone mean little, a time of use has to be included, for example a 100W load for 6 hours is 600Wh, or 0.6Kwh. Checking consumption with a kill-a-watt meter using grid power for each device is invaluable information to establish a figure.
1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
24 volt inverter will require 2 or 4 of those 12 marine RV batteries. 3 batteries cant be configured into a 24 volt bank. Better option would be 6 volt deep cycle batteries. 6 volt golf cart batteries work well for a starter set. They are very reasonably priced. Check Costco or Walmart.
We need a clearer description of your panels. 36 volt could be open circuit voltage, Voc,, which would equate to 60 cell panels. 36 Vmp. would equate to 72 cell (24 volt nominal) panels. This info is needed to configure your array and choose a charge controller.
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
Again loads before hardware, no point in discussing battery requiments or voltage, array size, or the array voltage, without addressing loads first, loads are what determine the ballance of system, it's as simple as that, no offense implied.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
mcgivor said:Again loads before hardware, no point in discussing battery requiments or voltage, array size, or the array voltage, without addressing loads first, loads are what determine the ballance of system, it's as simple as that, no offense implied.
Totally agree, none taken. Just putting a few thoughts out there. The lack of details and confusion of what a 24 volt panel is seems to be a common denominator with the "I've never done this before" crowd. From the op's posting it sounds like he fits that description pretty well. I'm not jumping in to help design his system. Probably shouldn't have used the term "We"2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
+1 on getting a better handle on loads. In addition to getting numbers for daily watt-hour consumption and peak consumption in watts, it would help to know if the van will have rv type DC loads (eg water pressure or lighting).
As you appear to have panels already, it would help to post specs from the sticker on the back - ie; Voc, Vmp, Isc, and Imp.
Will you have a separate generator and charger, or will you run the van engine for charging in bad weather and/or heavier use of loads?Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Already had solar which have no label/sticker. Will check with factory and post Voc, Vmp…
Presently I use alternator, small inverters 12V 700-1000W and many old junk batteries, smart charger, to run tools few hours.
Frig: 200W, .4Kw peak, load 2Kwh
A/C: 450W, .8Kw pk, load 3.6Kwh
Microwave: 700W, 2.8Kw pk, load .7Kwh
Alternative DC stove 200W, .2Kw pk, load .2Kwh
And 3 cups rice cooker, 200W, .25Kw pk, load .2Kwh
Or freeze dried foods.
Misc 50W, .05Kw pk, load .5Kwh
Drop computer, no heat water or pumps.
Total: 1.7-4.05Kw peak, load is 6.8-6.9Kwh
[1.7Kw peak for stove and rice cooker, 4.05Kw peak for microwave]
Without A/C: .9-3.25Kw peak, load is 3.2-3.3Kwh
-
The panel has 72 cells. It is no-load measurement, so probably it is 38Voc and 20Isc. I use Flute meter and another brand to measure. I was very surprised at first too, but it is possible.
-
Even without A/C, I'd suggest adding a generator. You would use the generator to bulk charge the batteries up to around 70% full in the morning, and to run A/C if needed after that. The panels could then finish charging in the mid-day sun.
I'm assuming 2x 36v means 2 panels, each with a Vmp around 36v and Imp around 8ish amps for an STC rating of around 300w. Real world will be about 75% of that with reasonable tilt and not scorching hot weather, so around 400w for a pair. I don't know where "1440w measured by the meter" comes from. Is this watt-hours over a day?Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Estragon, you are absolute right. I misunderstood solar calculation with measured 36V Voc x 20A Isc x 2 panels = 1440!
So depress to find one of the solar stickers with a note. Barely enough power to run a small frig. and a rice cooker or alike although DC water boiler and stove can run through cigarette lighter.
Will post tomorrow for help of the right controller and batteries.
Thanks.
-
solar spec:
4.8A Isc 34.4V Voc 600V Max
Rated 4.4A 34V 150W
hand written notes found: 170W (4.4Ax38Vmp)
Local solar radiation is about 6Kwh/m^2/day
Solar power supply estimate 2.46Kwh/day [.15Kw x 1.24 m^2 x 6 rad. x 2 panels]
Load 2.2Kwh and .5Kwp
Will this work?
Mppt 20A 12/24V, 95% efficiency
Battery 2x 12V 100A 2.4Kw
Keep same inverter 900W/1.3Kwp, efficient %?
-
I think you may be optimistic on pv production, but time will tell.
If the batteries are true deep cycle (not marine type), you can take them down to about 50% state of charge if recharging daily,;and still get a reasonable service life. If not true deep cycle, they won't last long doing that, as they'll be designed for brief, high current discharges and nearly immediate recharge. Even if you don't care about ruining the battery trying to use 100% of capacity, at low states of charge the voltage will drop off to a point the inverter won't work.
To get 2.4kw usable power with a good deep cycle battery, you need ~200ah@24v. That lets you take the 4.8kw bank to a 50% state of charge. 4x6v golf cart batteries for ~225ah@24v would be a reasonable choice.
Inverter efficiency varies with load. They tend to be reasonable (~85%) when running close to capacity, but can be not efficient at all when lightly loaded (eg running a couple of LED lights). A modified sine wave inverter may be about the same as pure sine wave running a resistive load (eg. rice cooker) but may have trouble running inductive loads (eg fridge) efficiently (or possibly running them at all).Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Thanks Estragon. You have plenty good knowledge of setting up camper van with solar. I learnt from you deep cycle 200A 24V to use 50% of battery capacity. Inverter can cut off 100A battery faster.
5 rad instead of 6 at my area from November to Spring.
My mistake again, load is 4.8Kwh for 200W frig [200x24]
With 85% efficiency, I can only use 1/2 day then charge by a generator, unless I can find another smaller frig 100W!!!
-
If you have propane on board already for cooking or heating, you might want to consider a propane fridge.
Another option might be to build a very well insulated box, and a Danfoss DC compressor and evaporator. I'm doing this for a dual compartment fridge/freezer at my cabin. Although not cheap, and involves labour to build the box, it should be very efficient. The first compartment more or less completed, uses about 200w/day at fridge temps, and about 350w/day at freezer temps.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
My mistake again! But very good news.
Annual maximum load is only 213-325Kwh or .89Kwh/day for a Frigidaire from the factory’s spec, not 200W x24hrs like I thought!
Presently I use compact propane stoves for camping, but solar will save a lot of time and dozens cans. I start making freeze-dry foods at home and plan to build my own machines and will use 3 more solar panels for this. So the frig is for fresh vegetable, fruits, drinks mostly. If I go fishing then I will consider a small freezer which is inexpensive around this area.
Calculate battery size:
890Wh / ( .85 efficiency x 24V battery)
50% state of charge results 87Ah or ~100Ah@24V battery.
I still like 200Ah to store more energy in case it needs and for summer, any disadvantage?
Will gauge 0 jump start cable wires work?
Thanks.
-
One of the problems with lead acid batteries is they simply need a lot of time under charge--Especially if the batteries are discharged by 50% or more. Generally, there are simply not enough hours in a sunny day to bring a 50% discharged bank back to 100% state of charge on a daily basis. Running 25% discharge per day (2 days to 50% state of charge) will give you a longer battery life (in general).
Placing some panels south west and south east (virtural tracking) will help extend the hours in a day...
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
I'm not a fan of using jumper clips as connectors. Something like Anderson connectors make for easy connection but safer and more reliable than clips. I would use the heaviest cable that will fit on the inverter, and keep it as short as possible. There needs to be a fuse or breaker on the positive (assuming negative ground) cable from battery to inverter.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Thanks for all value answers that help a lot. Now I can sure at least small Frig up running and hopefully a kettle/cooker on sunny days as well. There are a lot of sun hours here daily.
I have seen few solar power plants from the highway. Voltage was steady in 9 hours with the meter, I think of potential ~3Kwh, not 1 or 2Kwh, if the controller, wire and batteries are ready. And the mystic note of 170W from the plant engineers is 150W panel x (1m long x 1.13m wide) or 169.5W exactly.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 189 Solar Information links & sources, event announcements
- 886 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed