Grid tied solar array has voltage but no current
lindq530
Registered Users Posts: 9 ✭✭
I have a roof mounted grid tied system: 20 each Sharp ND-L3E1U panels (123W panels) connected in series and a Sunny Boy SWR2500U inverter. It's worked flawlessly for the last 15 years.
A couple of weeks ago I noticed that the the inverter display indicated that the array was producing 395V and 0 watts (I use the old fashion monitoring system of looking at the inverter display once a week or so). The voltage was consistent with historic values, but obviously the watts was not. Everything appeared to be working - except that I wasn't getting any power
I tried "rebooting" the system by turning off the AC and DC inputs. That didn't changing anything. I was fortunate to get an identical SB2500 inverter a few years ago form a working system that was being upgraded - I replaced the inverter and the results were the same - about 395 volts and no watts. I tested the continuity of the wires from AC connection to the house panel and the inverter to the roof - the wires are OK.
I visually inspected the panels and wiring connections and did not see any obvious issues.
The last thing I've tried is disconnecting each panel from the array and testing Voc and Isc using my multimeter. Every panel's output voltage was close to the the manufacturer's spec of 21.3V. Current output varied from 3-6A for each panel (I tried to measure the output in direct sun, but that was hard due to time constraints - spec is 8.1A). I have not tested each panel under load (because I'm trying to avoid that until its absolutely necessary).
I've read on this and other forums that I might have a panel that has failed. If so, the failed panel is letting a small amount of current pass so I get voltage, but not enough current to pass to produce measurable watts.
Any suggestions about what is causing the issue?
If it is a bad panel, any suggestions on how to identify the bad panel without dismantling and load testing each panel?
Thanks in advance for your comments and suggestions.
A couple of weeks ago I noticed that the the inverter display indicated that the array was producing 395V and 0 watts (I use the old fashion monitoring system of looking at the inverter display once a week or so). The voltage was consistent with historic values, but obviously the watts was not. Everything appeared to be working - except that I wasn't getting any power
I tried "rebooting" the system by turning off the AC and DC inputs. That didn't changing anything. I was fortunate to get an identical SB2500 inverter a few years ago form a working system that was being upgraded - I replaced the inverter and the results were the same - about 395 volts and no watts. I tested the continuity of the wires from AC connection to the house panel and the inverter to the roof - the wires are OK.
I visually inspected the panels and wiring connections and did not see any obvious issues.
The last thing I've tried is disconnecting each panel from the array and testing Voc and Isc using my multimeter. Every panel's output voltage was close to the the manufacturer's spec of 21.3V. Current output varied from 3-6A for each panel (I tried to measure the output in direct sun, but that was hard due to time constraints - spec is 8.1A). I have not tested each panel under load (because I'm trying to avoid that until its absolutely necessary).
I've read on this and other forums that I might have a panel that has failed. If so, the failed panel is letting a small amount of current pass so I get voltage, but not enough current to pass to produce measurable watts.
Any suggestions about what is causing the issue?
If it is a bad panel, any suggestions on how to identify the bad panel without dismantling and load testing each panel?
Thanks in advance for your comments and suggestions.
Comments
-
Have you checked the grid voltage and frequency, any inverter error codes? To search for a bad panel a pair of mc4 cables could be used to bypass one panel at a time, remember to disconnect the load to prevent possible arcing.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
mcgivor said:Have you checked the grid voltage and frequency, any inverter error codes? To search for a bad panel a pair of mc4 cables could be used to bypass one panel at a time, remember to disconnect the load to prevent possible arcing.
I may be at the point of isolating each panel with bypass cables. It will be a pain in the behind because of the how the panels are arranged, but it might be my last and final option. -
Update:
I measured the Isc of the total array (18 panels are still on the roof - I disconnected two panels to provide safe access) - measured about 6.5 amps with my clamp on meter. Voc was about 330V. That matched panel specs.
I finally resorted to the hardest option yet - bypassing individual panels. I thought I'd find a bad panel - when the bad panel was removed from the array I'd get watts. I used a jumper cable to bypass each panel individually. Each time I would bypass a panel, I would restart the system (it took about 4 hours). Each time the system voltage would be about 18 volts lower (as expected because of the array missing a panel) and still zero watts. It appears its not a bad panel.
When I measure the voltage of the array leads (with the inverter connected and on) I get:
Pos-neg: 330V
Pos - ground: 330V
Neg - ground: 0.0V
It doesn't appear I have a ground fault.
Everything points to the inverter being bad. I'm having trouble accepting that because one of the first things I did was replace the inverter. It seems very unlikely that two separate inverters would have the same issue.
I'm out of ideas.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 622 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed