Am I losing amps?
Qfwfq
Registered Users, Users Awaiting Email Confirmation Posts: 2 ✭
I'm about to add more power to my solar array and it occurred to me that this might not work as intended.
I am upgrading from 1kw@24v to 2.8kw@48v.
My charge controller is a 60a mmpt that can do 12v/24v/48v both in and out and my battery bank is 600ah@24v.
So my question is this - if I am getting ~60a@48v input, my battery bank/system is wired at 24v, and my charge controller has a max of 60a output.... what is happening to the other amps? SImple ohms law states 60a@48 = 120a@24v - but I know the charge controller can't do more than 60a... so whats going to happen and do I need to redo my whole system electrical system?
Thank you
I am upgrading from 1kw@24v to 2.8kw@48v.
My charge controller is a 60a mmpt that can do 12v/24v/48v both in and out and my battery bank is 600ah@24v.
So my question is this - if I am getting ~60a@48v input, my battery bank/system is wired at 24v, and my charge controller has a max of 60a output.... what is happening to the other amps? SImple ohms law states 60a@48 = 120a@24v - but I know the charge controller can't do more than 60a... so whats going to happen and do I need to redo my whole system electrical system?
Thank you
Comments
-
The charge controller limit means it will only draw ~30a at 48v from the array.
One option would be to add another controller to use more of the array capacity if you can use the extra power. This woukd also give some redundancy for when a controller fails.
Another might be to rewire the bank for 48v depending on what format the batteries are now (eg if you have 2 parallel strings at 24v now). You would likely have to replace your inverter though.
A third option would be to stay with the one controller. 60a into a 600ah bank isn't bad. Having extra pv would help get max power during light overcast days.
It really depends on your reasons for adding panels. If you have loads that can use the extra, but not high amp ones that justify 48v, adding a controller may be best. If you're running high draw loads like pumps, the second may be best. If you're just finding the smaller array isn't charging well on light cloud days, the third may be best.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
uhhgg
I do have two parallel strings of batteries at 24v so I could tie them together at 48v - but then my inverter wont work and that was/is one of the more expensive components of my system and I really don't want to replace a perfectly good unit.
maybe I will look into purchasing a small cheap mmpt controller and split the load.
The reason for upgrading is that I need the extra watts - for some reason I never considered that 60a@48v != 60a@24v
-
Charge Controllers (CCs) are usually rated for output current to the battery/inverter.
60 Amps IS 60 Amps. If you double the system voltage, the amount of POWER that the CC can deliver is doubled, if the CC has the capability to charge the higher voltage battery. (24 X 60 = 1440 Watts, 48 X 60 = 2880 W, as an example).
Of course, it is generally not a good idea to try to run power systems at their maximum capability continuously.
Vic
Off Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes. 25 KVA Polyphase Kubota diesel, Honda Eu6500isa, Eu3000is-es, Eu2000, Eu1000 gensets. Thanks Wind-Sun for this great Forum. -
Rewireing to 48V bank will give your controller full access to the larger PV array power. The amps for the controller is OUTPUT amps.
But you would need a new inverter.. There is no "small, cheap, MPPT" controller
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister ,
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed