What would happen if I used my old 8D's with my new 8D's?
Comments
-
Marc Kurth said:@softdown:
I do a LOT of 24/48/72, 2v cell strings for 48v AGM battery banks. When I speak with the Chief Engineer at a particular battery manufacturer about variations in individual cell voltages, he invariably responds with: "Marc, what are the individual cell voltages in a 48v bank with 8D's?" He goes on to explina that the same thing happens internally with a 6v, 8v or 12v battery. Please note that this applies to batteries of the same type and vintage.
After a lot of years doing this, I have become a huge believer in long float time to let batteries reach the same level.
Marc
First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries -
"Break in" involves draining some energy and putting it back. Roughly a dozen partial cycles will bring your batteries up to full capacity. Don't focus on precise standing voltages until then.
I meant allowing a good long (8-12 hours) float time every week or two (or more often!) in normal operation. This is an opinion coming only from field time with a whole lot of battery banks over the last 9-10 years - and hearing the same thing from folks way smarter than I.
Marc
I always have more questions than answers. That's the nature of life. -
Marc Kurth said:"Break in" involves draining some energy and putting it back. Roughly a dozen partial cycles will bring your batteries up to full capacity. Don't focus on precise standing voltages until then.
I meant allowing a good long (8-12 hours) float time every week or two (or more often!) in normal operation. This is an opinion coming only from field time with a whole lot of battery banks over the last 9-10 years - and hearing the same thing from folks way smarter than I.
Marc
FWIW....this mornings voltage started at 49.2 volts. Not good and not bad. Hard to judge when the rain robs one of several hours of float. Plus the batteries are not broken in yet.
First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries -
> @softdown said:
> Now the old 8D readings have become interesting:
> The battery with the positive charging cable is reading 14.3. Mfd in late 2011 and placed in service in early 2015.
> The battery with the negative charging cable is reading 13.02. Mfd in 2016, my newest battery.
> The other two old batteries are reading 13.7.
>
> I have always found very strong correlations between SG and voltage. Willing to bet the old battery now has higher SG readings. Also wondering if a weaker battery accepts a higher charging voltage more readily. Perhaps this high "float voltage" will disappear after the sun hands the duty baton over to the moon? I will probably report on findings.
>
> Running the RJ5 temperature sensor through foot thick walls was absolutely 2 1/2 bi**hes. Impossible without a wire puller, tape, and vaseline. Even removing vaseline impregnated tape was tricky.
I use a drill bit with a hole in it to pull wires through walls. Just drill, leave the bit in the wall, go thread a wire through the hole in the bit and use that to connect to the wire you are pulling. Then go back around again and pull it right through.
It makes life very easy.
https://www.amazon.com/gp/aw/d/B00004YO6E/ref=mp_s_a_1_3?ie=UTF8&qid=1501172558&sr=8-3&pi=AC_SX236_SY340_FMwebp_QL65&keywords=18+inch+drill+bit&dpPl=1&dpID=31MN+Qdi-kL&ref=plSrch -
softdown said:Marc Kurth said:"Break in" involves draining some energy and putting it back. Roughly a dozen partial cycles will bring your batteries up to full capacity. Don't focus on precise standing voltages until then.
I meant allowing a good long (8-12 hours) float time every week or two (or more often!) in normal operation. This is an opinion coming only from field time with a whole lot of battery banks over the last 9-10 years - and hearing the same thing from folks way smarter than I.
Marc
FWIW....this mornings voltage started at 49.2 volts. Not good and not bad. Hard to judge when the rain robs one of several hours of float. Plus the batteries are not broken in yet.
You bought them for a great price - use them now and save up to buy more later. Who knows, Elon seems to think that Lithium might be almost free by then
Marc
I always have more questions than answers. That's the nature of life. -
Solray said:> @softdown said:
> Now the old 8D readings have become interesting:
> The battery with the positive charging cable is reading 14.3. Mfd in late 2011 and placed in service in early 2015.
> The battery with the negative charging cable is reading 13.02. Mfd in 2016, my newest battery.
> The other two old batteries are reading 13.7.
>
> I have always found very strong correlations between SG and voltage. Willing to bet the old battery now has higher SG readings. Also wondering if a weaker battery accepts a higher charging voltage more readily. Perhaps this high "float voltage" will disappear after the sun hands the duty baton over to the moon? I will probably report on findings.
>
> Running the RJ5 temperature sensor through foot thick walls was absolutely 2 1/2 bi**hes. Impossible without a wire puller, tape, and vaseline. Even removing vaseline impregnated tape was tricky.
I use a drill bit with a hole in it to pull wires through walls. Just drill, leave the bit in the wall, go thread a wire through the hole in the bit and use that to connect to the wire you are pulling. Then go back around again and pull it right through.
It makes life very easy.
https://www.amazon.com/gp/aw/d/B00004YO6E/ref=mp_s_a_1_3?ie=UTF8&qid=1501172558&sr=8-3&pi=AC_SX236_SY340_FMwebp_QL65&keywords=18+inch+drill+bit&dpPl=1&dpID=31MN+Qdi-kL&ref=plSrch
Lest someone fail to notice the sarcasm, I did that once. Imagine my shock to find the insulation had been drilled away and the copper wiring exposed and shorting out.
First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries -
Marc Kurth said:softdown said:Marc Kurth said:"Break in" involves draining some energy and putting it back. Roughly a dozen partial cycles will bring your batteries up to full capacity. Don't focus on precise standing voltages until then.
I meant allowing a good long (8-12 hours) float time every week or two (or more often!) in normal operation. This is an opinion coming only from field time with a whole lot of battery banks over the last 9-10 years - and hearing the same thing from folks way smarter than I.
Marc
FWIW....this mornings voltage started at 49.2 volts. Not good and not bad. Hard to judge when the rain robs one of several hours of float. Plus the batteries are not broken in yet.
You bought them for a great price - use them now and save up to buy more later. Who knows, Elon seems to think that Lithium might be almost free by then
Marc
Call me bull headed, but I enjoy getting more life out of seven old 8D FLA's with very little resale value at all. They do fine... until a cell "shorts out". Curiously my old battery with two bad cells took a full charge. I will test the voltage tomorrow.
So the 1am power outage remains a major curiosity. What happened that day? I was gone for half of it, perhaps my security systems have become huge power consumers.
First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries -
softdown said:Solray said:> @softdown said:
> Now the old 8D readings have become interesting:
> The battery with the positive charging cable is reading 14.3. Mfd in late 2011 and placed in service in early 2015.
> The battery with the negative charging cable is reading 13.02. Mfd in 2016, my newest battery.
> The other two old batteries are reading 13.7.
>
> I have always found very strong correlations between SG and voltage. Willing to bet the old battery now has higher SG readings. Also wondering if a weaker battery accepts a higher charging voltage more readily. Perhaps this high "float voltage" will disappear after the sun hands the duty baton over to the moon? I will probably report on findings.
>
> Running the RJ5 temperature sensor through foot thick walls was absolutely 2 1/2 bi**hes. Impossible without a wire puller, tape, and vaseline. Even removing vaseline impregnated tape was tricky.
I use a drill bit with a hole in it to pull wires through walls. Just drill, leave the bit in the wall, go thread a wire through the hole in the bit and use that to connect to the wire you are pulling. Then go back around again and pull it right through.
It makes life very easy.
https://www.amazon.com/gp/aw/d/B00004YO6E/ref=mp_s_a_1_3?ie=UTF8&qid=1501172558&sr=8-3&pi=AC_SX236_SY340_FMwebp_QL65&keywords=18+inch+drill+bit&dpPl=1&dpID=31MN+Qdi-kL&ref=plSrch
Lest someone fail to notice the sarcasm, I did that once. Imagine my shock to find the insulation had been drilled away and the copper wiring exposed and shorting out. -
This mornings voltage shows 50.1 volts. That is what I had hoped to achieve. It is now quite possible that the old 8D's will quit developing bad cells every ~1/2 year. In celebration I turned the fridge/freezer down a couple degrees yesterday.
Having a powerful battery bank is awesome. Highly recommended.
Though my Outback MATE SOC meter crapped out while I was in the vicinity. It now seems to think that I have a 51% SOC and have not had fully charged batteries in 2.7 days. All that in spite of showing 50.1 volts at 5:30am. Electronics and I simply don't get along that great.
First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries -
1am power outage no longer a mystery. In spite of "taking a charge" yesterday, the questionable battery is now showing 8.5 volts....two bad cells indeed. Why did the charger still "charge it"? It almost always revolts against charging batteries with a bad cell.
First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries -
FWIW, my Johnson Controls 8D's built in 2011 have provided much better service than later years. My weakest battery is the second newest. Have several 2011 vintage still going strong.
First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries -
> @softdown said:
> 1am power outage no longer a mystery. In spite of "taking a charge" yesterday, the questionable battery is now showing 8.5 volts....two bad cells indeed. Why did the charger still "charge it"? It almost always revolts against charging batteries with a bad cell.
Bad charger too maybe. -
softdown said:1am power outage no longer a mystery. In spite of "taking a charge" yesterday, the questionable battery is now showing 8.5 volts....two bad cells indeed. Why did the charger still "charge it"? It almost always revolts against charging batteries with a bad cell.
I do not recall what you have.
I always have more questions than answers. That's the nature of life. -
Marc Kurth said:softdown said:1am power outage no longer a mystery. In spite of "taking a charge" yesterday, the questionable battery is now showing 8.5 volts....two bad cells indeed. Why did the charger still "charge it"? It almost always revolts against charging batteries with a bad cell.
I do not recall what you have.
I have no idea if the "desulfator" function works or not. I used to think it helped. Now I just try to keep batteries at 12.6 volts or better. After the battery is fully charged, it goes into a flashing "desulfate" mode.
Two of the cells in the bad 8D showed "water". I often double check stuff. Intermittent problems are everybody's delight?
First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries -
FWIW and hardly worth mentioning, Sam's Club has switched from Johnson Controls in Mexico to East Penn which is made of "imported and domestic" materials. The rep felt that Johnson quality had deteriorated significantly. That was also my experience though I can not offer a scientific sample.
First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries
Categories
- All Categories
- 220 Forum & Website
- 128 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed