100 watt solar panels
Comments
-
Sounds like one of the panels has a problem. Can you hook each one of them up in series with one of the other panels? This should allow you to weed out the bad panel. If you can determine which is the bad panel you ought to try to get it replaced under warranty.
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
it just the windy nation ones i tested the voc and isc and when not hooked up they seem ok but just soon as i hook them up they dont produce much power. got me a little confused cus the other pairs work just fine
-
Isc. and Voc. is not under any kind of load. Can you get a automotive brake light bulb or some other 12 volt load and test each panel individually?
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
Maybe the windy nation panels are a bit lower vmp than the others?Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
both renogy and windy nation panels vmp are like 17.6 range not sure on the missouri ones but the put out the amps i think they should. just so most understand if i mix one of the windy nation panels with another panel it kills the amp out put too when hooked up to charge controller . and on another note i looked at the diode and measured them they looked and measured the same
-
You need loads to draw maximum current from the array.
Either the battery bank needs to be under ~85% state of charge, or your load needs to be greater than Imp of the array. Or a combination of the two.
If the charge controller does not think the batteries need the full current (not in bulk stage but in absorb stage).
Basically, the charger needs to be in bulk mode and see around 13.6 volts or less at the battery so that it allows full current from the array.
- BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
bb i understood that . that why i tested the 3 sets of panels with in a minutes of each other so there wouldn't be that big of a difference in readings, when i tested the renogy/missouri panels they all were 5,5 amps or better and the windy nation ones read only 1.09 amps
-
So you unhooked 2 of the 3 pairs in sequence to do the test, with a single pair connected to the controller?
If so, my guess is a faulty connection somewhere.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Sounds like bad diodes bypassing strings of cells within the panel, if everything else looks good, try removing the diodes for a temporary test, HINT, take a picture to record the orientation, without the diodes in place, full output would be revealed, at least then you would know if in fact the cells are good, diodes are cheap to replace.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
Dcmike said:bb i understood that . that why i tested the 3 sets of panels with in a minute of each other
You said "Tracer." MPPT, right? I don't know the gory details on the algorithm it uses, but you may have to leave each set hooked up longer than "within a minute" to let it do a full sweep. Perhaps it did a sweep while the panels were disconnected, came up with a not-so-good solution, and kept that when the Windy Nation panels were connected? -
just today i did another test of the panels and i used a victron blue mppt charge controller (it has a pretty instant scan mode) and got same results as yesterday basically. when i hooked up the 2 windy nation panels i got 30 some volts and 1.9 amp but only 28 watts. hooked the 4 year old Missouri wind panels and bang i got 175 watts 30 some volts and 8.5 amps . im gonna look at the cells on the panels today and see if any thing is burnt and that why they dont work right . one good note windy nation is sending me one panel they for think is bad
-
Dcmike said:when i hooked up the 2 windy nation panels i got 30 some volts and 1.9 amp but only 28 watts.
30 V x 1.9 A = 57 W, not 28 W.
30 V x 8.5 A = 255 W, not 175 W.
Where are those numbers coming from?
-
-
mike_s said:If you get reasonable Isc, I don't see how it can be a connection or blocking diode problem unless it's intermittent - since that proves the connections can carry full current. Same with Voc and bypass diodes - a shorted diode would reduce Voc, and an open one would have no effect unless the panel were shaded.
Diodes generally fail short circuit but don't necessarily fail completely, there can be deterioration over time resulting in partially shorted diode, this would appear as reduced current, but not necessarily lower VOC. Temporarily removing the diodes would eliminate the possibility of a partial bypass, revealing the actual current the panel can supply, if it is still low, then possible cell damage has occurred. Always replace the diodes after testing.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
mcgivor said:Diodes generally fail short circuit but don't necessarily fail completely, there can be deterioration over time resulting in partially shorted diode, this would appear as reduced current, but not necessarily lower VOC.
-
Dcmike said:the victron blue software
-
mike_s said:mcgivor said:
Diodes generally fail short circuit but don't necessarily fail completely, there can be deterioration over time resulting in partially shorted diode, this would appear as reduced current, but not necessarily lower VOC.
Working with second hand information in a ping pong communication is difficult, especially when it seems that things don't look right, my suggestions are a means, through process of elimination, to determine what the problem is, an offer of help, which can be accepted or ignored, it's just what I would do in similar circumstances. Not being there, I can neither confirm nor deny what the instruments used, recorded, I can however say, electronic components can mislead one into believing the instruments used are correct, when in fact they are not 40 plus years of experience has shown me that things are not always what they seem. Personally I would want to know why something doesn't work, knowledge is earned and information is not knowledge. There is no intention to insult your comment, in fact all coments are valuable, if they are positive.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
mike_s said:Dcmike said:the victron blue software
-
Have you isolated the bad panel yet?
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
littleharbor2 said:Have you isolated the bad panel yet?
-
Are you going to provide details, or just let us keep guessing?
Making the assumption that it's a 12 V system, using lead acid batteries, one wonders why it's floating at 16 V. Anyway, since it's floating not charging, it only takes minimal current to hold the voltage so it's not a valid indication of what the panels are capable of. As has been mentioned multiple times, you need to put a load on it if you want to see what the panels can do. -
well the details on the my 1st post on the 24 volt system is 2 agm 155ah battery's now the victon blue mppt is on a lithium battery pack that i did not wanna say about because it erks to many when you mention lithium battery's .
-
Did you try to put a load on both of those panels? That would easily weed out any problems.
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
littleharbor2 said:Did you try to put a load on both of those panels? That would easily weed out any problems.
-
So you hooked up one at a time?
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
littleharbor2 said:So you hooked up one at a time?
-
OK, good to know. I now wonder if Windy nation has a problem run of panels. Two bad panels is unlikely unless a problem batch or there was some catastrophic event took them out.
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
well with 100 watts panels getting so cheap and most made in china, i wouldn't doubt they have a bad run of them every now and then
-
12 volt panels are still relatively expensive. I have 285 watt 24 volt panels for $100.00 and can hardly sell them now that the price of larger panels have dropped so low.
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
i so wanted to get 24 volt panels but the dang truck shipping is to much. so i just stick with 100 watt panels
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 622 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed