CC weirdness
Am I missing something or are CC makers just ignorant of wire size, connector space requirements?
Comments
-
Which controller?Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
i would fuse or circuit breaker then smaller wire to controler.
ThomOff grid since 1984. 430w of panel, 300w suresine , 4 gc batteries 12v system, Rogue mpt3024 charge controller , air breeze windmill, Mikita 2400w generator . Added 2@ 100w panel with a midnight brat -
There are many different crimp lugs for #10 - 12 AWG cable.
https://www.waytekwire.com/products/1434/Spade-Terminals/&Gauge=12-10
The above search term may expire in a fairly short time ...
Perhaps you have chosen a lug that was designed for a larger stud, or screw.YES, please do tell us which CC you are using. It is a bit surprising that the CC needs a spade lug (or a Ring lug), at all.
You might also look at the CC manual, carefully. It could specify just what they had in mind for those connections.
FWIW, Vic
Off Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes. 25 KVA Polyphase Kubota diesel, Honda Eu6500isa, Eu3000is-es, Eu2000, Eu1000 gensets. Thanks Wind-Sun for this great Forum. -
Morningstar generally is pretty good with regards to terminals and such, perhaps there is a maximum wire size allowable , small CC??
Details are always helpful. ...1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
It's the Morningstar Sunlight 20. I like using the closed end spade lugs rather than the "U" forked type because a closed end cannot slip out if a screw comes loose, I found some "U" type that can handle 10 gauge but not closed types.
-
A Flanged Spade Connector will get you most of what you want. Take a look at the side profile pic
https://www.waytekwire.com/item/32722/Molex-19125-0078-Flanged-Spade-Connector-/
-
Out of curiosity, by a closed "spade type " are you referring to a ring terminal, a fork flanged, or straight fork?, generally a spade terminal, is a flat interference type connector which has no screw, if insulated they would have colors (colours) red, blue or yellow as a reference to the appropriate gauge range of conductor the terminal can accommodate.Red- 22 to 16 gaugeBlue- 16-14 gaugeYellow- 12-10 gauge1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
Thanks Gary for the info on your CC.
There is no photo in the Manual for that CC, but from the outline drawing, it looks like there is a terminal block that accepts stripped bare copper wire, which is fairly standard for CCs.
In the manual there is the following'
• The connector terminals will accept a maximum wire size of
"AWG #10 (up to 5.2 mm2). A flathead screwdriver is required.
(Some #10 spade connectors may not fit in this terminal.) "
You might investigate further to see if stripped cable will fit into the terminals.If you could post a pic of the terminal connections of this CC, it would help.Thanks, VicOff Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes. 25 KVA Polyphase Kubota diesel, Honda Eu6500isa, Eu3000is-es, Eu2000, Eu1000 gensets. Thanks Wind-Sun for this great Forum. -
Vic, it's just an older version of this Morningstar CC:
https://www.solar-electric.com/ss-20l.htmlDoD= depth of discharge= amount removed from that battery SoC= state of charge= amount remaining in that batterySo, 0% DoD= 100% SoC, 25% DoD= 75% SoC, 50% DoD= 50% SoC, 75% DoD= 25% SoC, 100% DoD= 0% SoCA/C= air conditioning AC= alternating current (what comes from the outlets in your home) DC= direct current (what batteries & solar panels use) -
Myocardia, that's it. Vic, I didn't want to use bare wires, I'm much more comfortable with crimped, soldered terminals that I can put heat shrink on the crimp sleeve. I found some of the "U" style that may be a better fit but I'll wind up forming the end of the lugs around the screw to make a more positive connection. Failing that, I'll tin the wire ends and loop it into a "J" which will make it less likely to come out.
-
If you're really intent on using a termination, maybe use a ferrule?Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed