Help with wire length to load
n_yohan
n_yohan Registered Users Posts: 4
I'm confused. Please see picture below...
 I have three 12v batteries in parallel like below.  The wires going from each battery are the same length but my question is about the wire length going to the Load, also the charger.
Questions
1. Should the wires be the same length going to the load like B or shortest path like A?
2. Same question but this time the length of wires going to the charger..
3. I have a solar charger, AC charger/inverter, and of course the load.  Is it ok to have all three use a common path back to the battery bank (in the picture imagine the Load box as a common point that all three are wired to solar charger, inverter, load) or should they all have their own set of wires all the way back to the battery terminals?
Thanks so much for your help!!!
  • mcgivor
    1 Positive and negative same length as in B
    2 Same applies equal  length to the same terminals as load.
    3 Common point is fine
    Don't forget protection, fuses/circuit breakers
  • Solray
    Solray Registered Users Posts: 246 ✭✭✭
    Sort of like both. As short as possible and equal lengths. Avoid loops and coils.
  • rgk1
    rgk1 Solar Expert Posts: 135 ✭✭✭
    While on the subject, does the same rule apply if the batteries are in series?
    4-Risen 320 watt in series/parallel, 8-215ah 6 volt GC2 batteries in series, Exeltech 1100 watt/48 volt inverter, Tristar 45 MPPT controller.
  • mcgivor
    Same rules, position your batteries in a U rather than a straight line to keep your conductors as short as possible.
  • Horsefly
    Horsefly Registered Users Posts: 476 ✭✭✭✭
    Think of it this way: If batteries are parallel, you want the path from any battery out to your loads and back into that same battery to be the same length across all batteries. So the larger + and - wires don't have to be the same length, but the way you position the batteries so that the interconnects make it so each battery has the same path length is what is important.
    If you batteries are in series none of that matters, since every electron will have to travel the same distance out of the bank, around the loop, and back to the same battery.  You don't need to worry about any wires being the same length.
    In both cases you want the total length of the wires to be as short as possible just to minimize resistive losses.
    @BB. has posted a link several times that provides a good explanation of how to wire batteries in parallel.
    Steve
    BB. Super Moderators, Administrators Posts: 33,687 admin
    A is fine. B is not needed and not useful.
    Here is a good link that explains the various parallel battery connection options:
  • Horsefly
    I should add: With three batteries connected kind of like you show in either diagram (like I said, either is fine), the middle battery has to deal with a slightly greater loss in the cabling than the ones on either end. It won't be much, assuming the cables between the batteries are plenty big and as short as possible. But the center battery will deliver slightly less current to the load than the other two. The only way to avoid that is to have all three batteries have the same short cables going to positive and negative buss bars, and have the longer cables to the load connect to the buss bars.
  • Solray
    'A' would be a lot better if the bank was set up parallel to the load instead of perpendicular. There is no good reason to have one of the batteries so far away.
  • n_yohan
    The reason the batteries are lined up like that is that they are in a camper van and there is some unused space that can fit three batteries end to end.
    If I had more space I would do it like you suggest.
  • Estragon
    You want to keep the circuit as short as possible. 'A' is as short as possible. 'B' adds wire for no good reason.
    Even if you turn the load, you might double the positive and half the negative, and still end up with the same amount of wire. I don't see how it makes any difference.
  • Solray
    If you can end up with a shorter total length it does make a difference.
  • Estragon
    Shorter total (circuit) length, yes. Whether the + or - is longer than the other, no?
  • Solray
    No. :)