Schneider Electric Conext SW 4048 Hybrid Inverter with AC Support multiple problems

My solar system configuration is:
1.Conext SW 4048 220V inverter.
2. Conext MPPT 60 PV charger
3. 200Ah 48V battery bank.
4. 1.5kW solar panels.
5. Conext ComBox for monitoring.
All devices have the firmware upgraded to the latest version.
I. First problem, and the biggest one is this:
"NOTE: To prevent injecting current into the grid from the inverter, there is less than 2 amps of offset allowed from the grid to flow into AC IN even when Load Shave Amps is set to 0" Documentation update on Schneider Electric website.
and this NOTE is translated to the following picture:
With full sun outside and for a 234W output load on AC i have a 255W input from the grid and ZERO input from the solar panels.
I hope there is a way to disable this 2 Amps offset, because this it's making the solar system useless, maybe a hidden service menu or a custom firmware update..? At this point i had to manually disconnect the grid from the inverter, in order to use the solar energy .
And with the latest firmware update you cannot set the load shave to 0, it is minimum 1 Amp, so a minimum of 3 Amps (660W ) must be drawn from the grid in order use solar energy.
II. The second problem:
Battery voltage readings and charging values are totally off by 1.5V !.
As you can see in the picture, the battery is in float charging with a set point of 53.8V. The MPPT it's reading 55.3V and the CSW 56.2V.
Also i measured the voltage with a calibrated multi-meter and i have 54.8V.
And some other issues with wrong power reporting...

And, not to forgot that the first ComBox failed after 6 hours! And they eventually replaced the unit under RMA, after 2 weeks...
1.Conext SW 4048 220V inverter.
2. Conext MPPT 60 PV charger
3. 200Ah 48V battery bank.
4. 1.5kW solar panels.
5. Conext ComBox for monitoring.
All devices have the firmware upgraded to the latest version.
I. First problem, and the biggest one is this:
"NOTE: To prevent injecting current into the grid from the inverter, there is less than 2 amps of offset allowed from the grid to flow into AC IN even when Load Shave Amps is set to 0" Documentation update on Schneider Electric website.
and this NOTE is translated to the following picture:

With full sun outside and for a 234W output load on AC i have a 255W input from the grid and ZERO input from the solar panels.
I hope there is a way to disable this 2 Amps offset, because this it's making the solar system useless, maybe a hidden service menu or a custom firmware update..? At this point i had to manually disconnect the grid from the inverter, in order to use the solar energy .
And with the latest firmware update you cannot set the load shave to 0, it is minimum 1 Amp, so a minimum of 3 Amps (660W ) must be drawn from the grid in order use solar energy.
II. The second problem:
Battery voltage readings and charging values are totally off by 1.5V !.
As you can see in the picture, the battery is in float charging with a set point of 53.8V. The MPPT it's reading 55.3V and the CSW 56.2V.
Also i measured the voltage with a calibrated multi-meter and i have 54.8V.
And some other issues with wrong power reporting...

And, not to forgot that the first ComBox failed after 6 hours! And they eventually replaced the unit under RMA, after 2 weeks...
Comments
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister ,
http://members.sti.net/offgridsolar/
E-mail [email protected]
I didn't show this to Schneider yet, the equipment it's new and was installed by me as the Install-Owners-Guide specifies.
It is helpful to post a picture of the electronics and battery. The more information you post the more helpful this can be.
Your location can help along with what you intend to do. Good Luck!
http://members.sti.net/offgridsolar/
E-mail [email protected]
At this time, between me and the solar system is a 100 mile distance, i can only do remote access to the ComBox, i'll add some pictures in the weekend.
And some detalils:
AWG 3 wires were used to connect the inverter to batteries, with maximum length of ~1m in order to reduce power loss.
AWG 5 wires used to connect the charger to batteries.
Newmax battery
The above picture it's with grid disconnected.
And current reporting from inverter it's oscillating from -3.5A and +3.5A.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
The 200ah is the 20 hour rate correct?
http://members.sti.net/offgridsolar/
E-mail [email protected]
I just measured the voltages again at battery terminal, inverter (no load) screw and MPPT connector, i have the same voltage with my multimeter in all 3 points, in this case is 50.9. Combox is saying 52V for inverter and 51.5 for MPPT.
Seems a calibration problem for me. Is there any way to calibrate these units ?
some people are using an ac 240 timer, in order to disconnect during sun hours and reconnect back to the grid at nigh time. but feels like money in the trash to buy an expensive inverter because all the features but can not do the one thing it was buy for.. to use sun energy every time its available
the old trace/xantrex SW was barely grid tie and mostly used for marine and rv applications
the XW series was specifically made for offgrid and gridtie or just plain backup power if you didnt have solar
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister ,
it will be nice to instead of a timer, automated the process using battery voltage, so the user/installer can set a desire battery voltage to cut the grid, and desire voltage to turn the grid back on.
for example, turn off the grid at 25Vdc, turn grid on at 24.5Vdc
http://members.sti.net/offgridsolar/
E-mail [email protected]
but... when it was advertised to work well, with a lot of features, bells and whistles...
why a client may choose an SW over the XW?
1. it was advertises to be the same, only smaller and without netmeterin
2. in PR its hard to get the netmeterin approved, the permit may be rejected by a lot of excuses from the utility without any logic reason.
3. there are sectors where the feeder is full so utility will not receive the interconnection application
4. there are clientes with small homes that their peak is just 1,500 w, and only consume 10 to 12kwh/day
5. last but not least.... it was advertises to work as good as the XW, only smaller, without netmetering and cheaper!!!
So, by the client side, it was a no brainer to choose an SW over an XW.
But... with all the experience and troubles the SW are giving... I am not recommending the SW no more... just for off grid applications or people that realy dont have the money for an XW installation, i first offer the XW if the client dont have the budget, then I offer the SW but listing all the limitations it have
http://www.electrodepot.com/contactor.htm
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
https://www.amazon.com/Pole-Programmable-Timer-Control-9344204/dp/B01GXYNMO2/ref=sr_1_4?s=hi&ie=UTF8&qid=1537460306&sr=1-4&keywords=timer+60+amp&dpID=41gljfaVgoL&preST=_SX300_QL70_&dpSrc=srch
if instead of a timer, some device that can be set to program it to open the contactor when the battery is at 90% DOC and close it when the battery is at 60% DOC, it will be even better! so user dont run out of batteries during rainy days
The 2 amp ~480W requirement is an issue, but the bigger issue I see is actually the balancing requirement. I can have a load of 1500W and I get 100W from the grid if 1 leg is only 500W. Even by rearranging my circuits trying to balance the load L1 and L2 Its nearly impossible to get decent self consumption on this inverter. I can have a bright sunny day and used 20KWH at home and i get 3 kwh from my 3500W solar array. I leave and my battery is 100% I come home and the battery is 100% and it used 3kwh
The only time I see a reasonable self consumption is when the well pump comes on and i have 240V and even load on both legs. Overall pretty unimpressed with this product and its marketing as a self consumption system. I often see 1500W load and only 200W coming from the solar. I switch the breaker off and my array output jumps 1500W. I turn on some more loads and the array has peaked at 3500W when the battery got low.
This unit, and solar system ~(9K$ self install) will NEVER pay for itself in self consumption. I get that grid tied would be best for payback, but the "hybrid" is really a lie - this system is terrible at self consumption. I wanted a hybrid that would provide battery backup needs here for potential weeks without power, but I wanted to actually get the system to pay for itself in 7 years.
The only way to get full usage from my array is to leave this system off and run off grid, but I find my night loads are too high, or cloudy days are potentially deep cycling so I either have to double or triple my battery bank, or cycle it really deep. By the time I get payback I will need a new battery bank from the deep cycling, and then reset the payback counter.
At the moment I am left turning the breaker on and off at 7 am and watching the weather to make sure my wife doesn't kill the battery with laundry/dishwasher/toaster oven/etc during the day while the breaker is off. I mostly err on the side of protecting the battery and miss out on solar. I can get 8-15 kwh generation from the array and the battery is full when I get home from work at 6:30 on a partly sunny day. on a cloudy day I have come home to low voltage warning.
I have been considering using the MPPT60 charge controllers analog output to drive a contactor on the AC input to the SW4048.
I was wondering if anyone has done this, and what the settings are that they used for the thresholds with AGM batteries?
If i use a normally closed contactor, and setup the analog output to turn on at say 53V, and power a 12V relay to drive the AC contactor I can make the unit go off grid when the solar output is good. If I set the threshold for turn off at 51V (with a 15 minute delay) I can have the unit automatically turn the AC back on when array drops out and the battery is loaded without solar input. The delay can prevent trips from high loads for short periods (well pump + etc) This is essentially what I do when I am home - I monitor the voltage and turn the breaker back on when the array output is low, but I am "working" for 1-2$ here a day and want to automate this to get a payback without having to work for it or think about it every day.
Anyone have a setup like this? is there a problem with the AC input turning on and off a few times a day for years? I think the debounce timer will help prevent it toggling too much if I set the thresholds right for the charge controller output.
Why can't schneider do this? I know there is a contactor inside the unit that does this very function ac when I switch AC on and OFF there is a delay before it uses the AC input, why cant they simply put the unit "really" off grid when the solar is really good?
I would appreciate any advice / feedback from this group, it looks like a nice community here.
One unimpressed SW4048 owner.......
Justin
There is alot of info on the forum here if you search it. This is really a job for an XW that does not get imbalanced by L1 and L2 loads.
http://members.sti.net/offgridsolar/
E-mail [email protected]
I have not updated firmware but have a build data from Dec 2021 my understanding is that I need a com box or other service tool to do the firmware.