Home UPS Overloads
sinner_93
Registered Users Posts: 5 ✭
My solar home system has a 200Ah LA battery, three 135 Wp panels in parallel, a MPPT charge controller, 900 VA Home UPS. I use it to light bulbs all over my house that has three floors, and sometimes charge my phones and laptops and run the internet router and the ONU device 24/7. Multiple times a day the UPS goes into overload without any huge loads. It happens during broad daylight when the battery is fully charged or at midnight when the battery is discharging or during the early morning when the battery is at it's lowest SoC. There's really no pattern to it.
But once I turn the UPS off and on back again it works without removing any devices plugged in although the overload led blinks for a few times before turning off completely. I've had the house wiring checked, battery gravity checked and the UPS serviced by the UPS company but to no avail. What could be the problem? Thanks in advance!
But once I turn the UPS off and on back again it works without removing any devices plugged in although the overload led blinks for a few times before turning off completely. I've had the house wiring checked, battery gravity checked and the UPS serviced by the UPS company but to no avail. What could be the problem? Thanks in advance!
Comments
-
One of your phones wouldn't be a Samsung note7 would it? Seriously though, it would help to establish if the overload is real. Do you have something like a kill-a-watt to check actual load?Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Haha, no. I like my house not on fire.
The whole house when lighting every single bulb and all the devices running is 200W - 250W and out of that I only light a fraction of the bulbs and run a few devices. I don't have a similar device but wouldn't the overload happen every time I turn the UPS on if that was the case?
One thing I did notice yesterday was that when I was charging the battery from the AC mains and when I turned the AC mains off the UPS went into overload again. It was late evening and the house was lit. -
Power Factor could be the cause.
A 5w LED bulb often has a cheap driver circuit and likely consumes 10VA . AC power is measured in Volt Amps, and totals the real power the devices use. The batteries only need supply the peak power, but the inverter has to be able to supply the real power.
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
The PF is one reason I suggested measuring actual loads rather than adding up rated amp on devices.
As well, maybe something got plugged in and forgotten about, or maybe something is drawing more power than it should, like a bad/failing wall wart. Some of those things seem to have internal heaters as undocumented features.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Some UPS do not like to be powered from the battery for an extended time. They are designed to draw power from the battery for a little time at a time and an extended use could overheat the electronics inside them, After all, you just powering an el cheapo build-in internal msw ( modified sine wave ) inverter that is designed to just run long enough to shut your computer down when there is a power failure.. Most UPS in my eyes are a bad choices to run electronics on them while they are running on battery power, they will eventually burn the electronic items up, like a msw inverter would.
I extended my battery to an 42 ahr capacity on my 1100 VA UPS and once a month I test the system which will be powered for 24 hrs from the extended battery capacity. While in test-mode the plastic casing of my UPS is getting very hot and I ended up to cut extra air slots in it to help it cooling it down. When in normal AC mode there is almost no heat what-so-ever, because you are just charging the battery with very little power and the standby power is very small also and will not develop a lot of heat.
Maybe you are dealing with an internal over temperature.
-
mike95490 said:Power Factor could be the cause.
A 5w LED bulb often has a cheap driver circuit and likely consumes 10VA . AC power is measured in Volt Amps, and totals the real power the devices use. The batteries only need supply the peak power, but the inverter has to be able to supply the real power. -
Estragon said:The PF is one reason I suggested measuring actual loads rather than adding up rated amp on devices.
As well, maybe something got plugged in and forgotten about, or maybe something is drawing more power than it should, like a bad/failing wall wart. Some of those things seem to have internal heaters as undocumented features. -
Johann said:Some UPS do not like to be powered from the battery for an extended time. They are designed to draw power from the battery for a little time at a time and an extended use could overheat the electronics inside them, After all, you just powering an el cheapo build-in internal msw ( modified sine wave ) inverter that is designed to just run long enough to shut your computer down when there is a power failure.. Most UPS in my eyes are a bad choices to run electronics on them while they are running on battery power, they will eventually burn the electronic items up, like a msw inverter would.
I extended my battery to an 42 ahr capacity on my 1100 VA UPS and once a month I test the system which will be powered for 24 hrs from the extended battery capacity. While in test-mode the plastic casing of my UPS is getting very hot and I ended up to cut extra air slots in it to help it cooling it down. When in normal AC mode there is almost no heat what-so-ever, because you are just charging the battery with very little power and the standby power is very small also and will not develop a lot of heat.
Maybe you are dealing with an internal over temperature. -
Some UPS systems will not turn on if the AC neutral is not bonded to Ground somewhere in the system (such as at the main panel or you use a smaller AC genset that has full floating AC output)... I .e., you have significant voltage between Neutral and Ground). Many of the ones I used required a manual button press on the front panel to "turn on" if the AC power cord was not plugged in.
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
A $20 investment in a kill-a-watt meter (NAWS sells them) might be a big help in chasing this down. It can tell you consumption both at a point in time and over a period of time.
Also a multimeter to check for the ground/neutral mentioned by Bill. Intermittent problems like this can be hard to isolate without the right tools.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems