Trimetric Question

RV system. I installed a Trimetric 2030 with the sc 2030 charge controller and the 500 amp shunt. I have two 135 watt Kyocera panels wired in parallel....but my question is when there is no dc load and charge the controller is off my Trimetric always shows a negative .1 or .2 reading. I disconnected the dc fuses one at a time to see if a circuit was drawing current but it made no difference. Thanks for any help.
Comments
- Assorted other systems, pieces and to many panels in the closet to not do more projects.
You may find a setting for the Trimetric to adjust the meter that reads the voltage drop across the shunt--Or they may have a "dead zone" adjustment (i.e., +0.2 amps to -0.2 amps reads zero on the meter).
Hmmm... Looking at the meter manual, you can adjust the Volts reading, but not the shunt current (microVolts) reading.
http://www.bogartengineering.com/wp-content/uploads/docs/TM-2030 Users Instructions11-01-16.pdf
Since it is not adjustable (that I can find)... Verify the meter is working correctly. You want good electrical connections on both ends of the shunt voltage meter wiring--If one end is loose/corroded/dirty, you may get some "stray voltages".
Take the two wires off the shunt and short them together--What does the Amp Meter read now?
Make sure that G1 (meter ground goes to the battery). And that Sense Ground goes to the system ground side Kelvin contact on the battery shunt.
http://www.bogartengineering.com/wp-content/uploads/docs/TM-2030Install Instructions.pdf
Lastly, G2 (sense ground) and Sense should be twisted pair wires ideally (keep magnetic interference from other devices/AC wiring/etc. from coupling into the microvolt meter of the shunt interface).
That is about all I can think of without calling the mfg. for support.
-Bill