Actual Output of an Array
ColoradoSolar
ColoradoSolar Registered Users Posts: 63 ✭✭
If I have an array of 12.15kW I know that I can't get all 12.15kW out of the array. If I want to determine the nominal watts I would have available what kind of factor would I need to use. Currently in my calculations I am using 80% so my 12.15kW array will give me a nominal output of 9.72kW. Is that a good factor to use for calculations?
Thanks,
Eric
    Eric, You should be able to look up your Normal Operating Cell Temperature Values (NOCT) These usually run about 75% of the panels rating, I guess you understand that their are other system losses.
  • ColoradoSolar
    I will look for the NOCT in the specs.
    Yes I understand there are many other losses in the system and I think I am taking care of them in my calculations.
    I use ~77% for Solar Panels through GT AC inverter (vs predicted hours of sun)--That will get you within 10% of your average output energy over time (a bit on the conservative side for colder climates--Hot panels produce less Vmp-array, and less power).
    For wiring and such... I always suggest a minimum of 1.25x your expected rated current to keep the wiring cooler and not have false trips on fuses and circuit breakers.... I.e., 15 amps continuous current in cable * 1.25 = 18.75 ~ 20 amp branch wiring+breaker ratings).
  • Estragon
    In Colorado, altitude may also be a factor. High altitude means less atmosphere for sun to get through and cooler temps means higher production.
  • ColoradoSolar
    I am in a high valley at 7800ft. The sun is crazy strong up here and the temps rarely get above 80 in the heat of the summer.
  • Estragon
    On a nice spring day with a breeze from the north keeping the back of the panels cool, you should see some pretty good output!
  • ColoradoSolar
    The only problem with the nice spring breezes here is that we almost always have wind and usually strong. Today it is showing 35mph gusting to 51mph, so I have to make sure my mounts are ready for the wind.