Actual Output of an Array

If I have an array of 12.15kW I know that I can't get all 12.15kW out of the array. If I want to determine the nominal watts I would have available what kind of factor would I need to use. Currently in my calculations I am using 80% so my 12.15kW array will give me a nominal output of 9.72kW. Is that a good factor to use for calculations?
Thanks,
Eric
Thanks,
Eric
Comments
- Assorted other systems, pieces and to many panels in the closet to not do more projects.
Yes I understand there are many other losses in the system and I think I am taking care of them in my calculations.
For wiring and such... I always suggest a minimum of 1.25x your expected rated current to keep the wiring cooler and not have false trips on fuses and circuit breakers.... I.e., 15 amps continuous current in cable * 1.25 = 18.75 ~ 20 amp branch wiring+breaker ratings).
-Bill