Parallel battery bank wiring diagram
drich5
drich5 Registered Users Posts: 7 ✭✭
I would like to know how to connect 8 12v batteries in parallel to achieve a perfectly balanced charge and draw.
    Perfect? Pretty much not going to happen.
    But assuming they are the same age, make and model, the idea to have the same resistance across each string. In this case a since you have so many strings, You should incorporate a busbar for each the positive and negative battery cables;
    Use the same length and gauge cables to connect each battery.
  • Mike 870
    Mike 870 Registered Users Posts: 42 ✭✭✭
    I've not personally tried this, but...   http://www.iotaengineering.com/pplib/balancedcharging.pdf
  • mvas
    mvas Registered Users Posts: 395 ✭✭✭
    And then use "opposite diagonal" method to connect the two main power cables to the Charger & Load ...
    The (+) main power cable connects to "top end" (near battery #1) of (+) copper bar
    The (-) main power cable connects to "bottom end" (near battery #8) of (-) copper bar.
  • littleharbor2
    edited February 2017 #5
    There is no "opposite diagonal" connection with a buss bar. Every battery gets it's own cables.
  • mvas
    Tthe how's and why's of connecting 4 batteries in Parallel ...
  • mvas
    edited February 2017 #7
    As I stated ...  there is opposite diagonal connections of the Main Power Cables for the Charger and the Load.
  • littleharbor2
    Last I checked everything connects to the buss bar. If anything the loads and charging connections would probably work best at the center of the bussbar.
  • mvas
    No, it is not best to connect Main Power Cables to the center of bus.
    It is best to connect the Main Power Cables at opposite diagonals.
  • littleharbor2
    Can you explain why?
    Took me a while to figure out what he was saying too! Connect the cables Main then battery 1, 2, 3, 4, 5,6,7,8 on one side, and batteries 1,2,3,4,5,6,7,8, then main on the other busbar to keep the resistance the same including the busbar.
  • littleharbor2
    I can see that making sense in a minute sort of way. A minute amount of resistance is all it takes to cause uneven charging. I see the buss bar as evenly energized but I'm admittedly no expert. Anybody else care to comment?
  • Estragon
    My guess is that the connections (battery posts and buss) are likely to be more of a problem than the buss itself in terms of resistance.
    In theory, theory and practice are the same. In practice, they rarely are ;-)
  • bill von novak
    bill von novak Solar Expert Posts: 892 ✭✭✭✭
    Agreed.  The reason people use busbars is because they can provide a common connection point with negligible differential resistance, and most busbars accomplish this.  Between differing torque on each nut, different surface conditions on each lug, different crimp quality on each cable etc. the resistance of the busbar itself will negligible.
  • drich5
    Okay good people, thanks for all your replies. "smartgauge" and "iotaengineering" both show the same diagram for a 4-battery string, perfectly balanced. However, I am having trouble imagining how to add the next 4 batteries, to complete a string of 8 batteries. My 2/0 cable is here now, so if someone has a diagram for 8, I will be forever in your debt.
