I live in Greece off grid and currently my setup is:
24v 450ah battery bank
4 x 235w 24v solarworld poly panels = 940 watts
Can please someone let me know if the current panels give enough power to my power bank? I would like to add 2 more panels but I cannot find the same make and wattage. Shall I go for higher wattage (lets say 250w) of the same brand or find the same wattage from another brand?
Many thanks in advance!!!
24v 450ah battery bank
4 x 235w 24v solarworld poly panels = 940 watts
Can please someone let me know if the current panels give enough power to my power bank? I would like to add 2 more panels but I cannot find the same make and wattage. Shall I go for higher wattage (lets say 250w) of the same brand or find the same wattage from another brand?
Many thanks in advance!!!
Comments
-
Are your panels getting the batteries fully charged at least once or twice per week? Are you able to get at least to absorb most days? Do you have a generator? Depending on loads, location, etc. your panels might be okay or not.
Assuming you have a MPPT charge controller capable of handling the extra current, you will want to add panels close in Vmp to your existing ones. Brand isn't all that important. Panel specs are.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
yiannis5 said:I live in Greece off grid and currently my setup is:
24v 450ah battery bank
4 x 235w 24v solarworld poly panels = 940 watts
Can please someone let me know if the current panels give enough power to my power bank? I would like to add 2 more panels but I cannot find the same make and wattage. Shall I go for higher wattage (lets say 250w) of the same brand or find the same wattage from another brand?
Many thanks in advance!!!1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
mcgivor said:yiannis5 said:I live in Greece off grid and currently my setup is:
24v 450ah battery bank
4 x 235w 24v solarworld poly panels = 940 watts
Can please someone let me know if the current panels give enough power to my power bank? I would like to add 2 more panels but I cannot find the same make and wattage. Shall I go for higher wattage (lets say 250w) of the same brand or find the same wattage from another brand?
Many thanks in advance!!! -
Estragon said:Are your panels getting the batteries fully charged at least once or twice per week? Are you able to get at least to absorb most days? Do you have a generator? Depending on loads, location, etc. your panels might be okay or not.
Assuming you have a MPPT charge controller capable of handling the extra current, you will want to add panels close in Vmp to your existing ones. Brand isn't all that important. Panel specs are. -
SW 235
Maximum power Pmax 235 Wp
Open circuit voltage Voc 37.0 V
Maximum power point voltage Vmpp 30.0 V
Short circuit current Isc 8.35 A
Maximum power point current Impp 7.85 A
OK... You have a 24 volt battery bank. I hope you have the array setup as 2x series by 2x parallel strings?
The normal range for charging your battery bank:- 450 AH * 29 volts charging * 1/0.77 panel+controller deratings * 0.05 rate of charge = 847 watt array minimum
- 450 AH * 29 volts charging * 1/0.77 panel+controller deratings * 0.05 rate of charge = 1,695 watt array nominal
- 450 AH * 29 volts charging * 1/0.77 panel+controller deratings * 0.05 rate of charge = 2,203 watt array "cost effective" maximum
Vmp~30 volts is common. Get any other panels (mono or poly crystalline, any good brand, "60 cell" panels) that you can put 2 in series (Vmp-array~60 volts), and you will be fine.
With 3 or more parallel strings, you should have a fuse/circuit breaker per string to reduce the chances of fire if one of the strings fails (broken panel, shorted wiring).
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset - 450 AH * 29 volts charging * 1/0.77 panel+controller deratings * 0.05 rate of charge = 847 watt array minimum
-
BB. said:SW 235
Maximum power Pmax 235 Wp
Open circuit voltage Voc 37.0 V
Maximum power point voltage Vmpp 30.0 V
Short circuit current Isc 8.35 A
Maximum power point current Impp 7.85 A
OK... You have a 24 volt battery bank. I hope you have the array setup as 2x series by 2x parallel strings?
The normal range for charging your battery bank:- 450 AH * 29 volts charging * 1/0.77 panel+controller deratings * 0.05 rate of charge = 847 watt array minimum
- 450 AH * 29 volts charging * 1/0.77 panel+controller deratings * 0.05 rate of charge = 1,695 watt array nominal
- 450 AH * 29 volts charging * 1/0.77 panel+controller deratings * 0.05 rate of charge = 2,203 watt array "cost effective" maximum
Vmp~30 volts is common. Get any other panels (mono or poly crystalline, any good brand, "60 cell" panels) that you can put 2 in series (Vmp-array~60 volts), and you will be fine.
With 3 or more parallel strings, you should have a fuse/circuit breaker per string to reduce the chances of fire if one of the strings fails (broken panel, shorted wiring).
-Bill - 450 AH * 29 volts charging * 1/0.77 panel+controller deratings * 0.05 rate of charge = 847 watt array minimum
-
As long as the parallel voltages are similar (within 5% good, within 10% will work), you can mix any wattage panels.
Roughly, the maximum array for a single 60 Amp MPPT controller:- 60 amps * 29 volts charging * 1/0.77 panel+controller derating = 2,260 Watt array max "cost effective" for 60 amp MPPT controller @ 24 volt battery bank
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
BB. said:As long as the parallel voltages are similar (within 5% good, within 10% will work), you can mix any wattage panels.
Roughly, the maximum array for a single 60 Amp MPPT controller:- 60 amps * 29 volts charging * 1/0.77 panel+controller derating = 2,260 Watt array max "cost effective" for 60 amp MPPT controller @ 24 volt battery bank
-Bill -
Generally, solar arrays (plus charge controller losses) output only (on average) a typical maximum power of ~77% of the array's rating. Vmp falls with hot solar panel temperatures--So in hot climates, the derating is more "real". In very cold climates/sub freezing, the Vmp rises, and can output more power through the MPPT controller (power = Voltage * Current, rising Vpanel, rising power).
Good quality MPPT controllers will limit their output current to the rated amount (60 amps), even if more power is available. No damage, just normal operation.
For most people, the charge controller will "clip" or limit output only a little bit on cool/clear days. Not usually enough to worry about.
Of course, if you want, you can always purchase another charge controller (or run the battery bank at 48 VDC).
1,500 Watts / 60 amps = 25.0 volts...
That is what is usually done (use derated solar array by 77%). If the manual says 1,500 Watts, then you will not go wrong either.
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Just to expand a bit on Bill's good advice - as you get close to the amp output limit of a charge controller it may make sense to consider a second controller for two reasons; first because working a single controller near max generates more heat, which can shorten electronics life, and second because adding a second controller makes life a lot easier when (not if) one controller dies.
It sounds like your batteries are fairly happy with the setup you have though, given your location and loads.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 622 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed