Choosing kAIC on PV inverters (AC Side)
squelchea
Registered Users Posts: 6 ✭✭
Hi Guyz,
on selecting PV inverter breaker, what will be my baseline on choosing its kAIC rating ? this refers to AC side breaker.
any formulas ?
thanks
any formulas ?
thanks
It almost doesn't matter. Breakers are designed to easily trip on overloads when Hover Dam is powering the circuit, An inverter is a "soft source" and may not always be able to trip a properly sized breaker, So you install breakers anyway, properly, but I don't know about a main output breaker. My inverter has a pretty beefy surge rating for motor starting, and may never be able to trip a breaker sized to pass the starting surge, Say it's a 10 amp rated, with 20A surge for 30 sec. How to size a breaker for that ??? (this is an example, not my actual spec)
Standard US AC breakers are 10,000 AIC rated. This is the designed Pole top transformer and AC drop to home's maximum current.
No home sized inverter or genset is going to come close to this amount of current...
10,000 Amps * 240 VAC = 2,400,000 Watts (VA) = 2.4 MWatts surge current
That is about 500 to 1,000x larger than the average off grid system's power capability.