Suggestion for 24 volt charger run off generator for back up
Dailypix
Registered Users Posts: 11 ✭✭
I recently changed over to a 24 volt system. Sometimes in winter (my off grid solar is in Northern Ontario) my panels do not generate enough power to keep the batteries charged. I get about 5 feet of snow sometimes in the snow belt and it is often cloudy. When I was on 12 volts I used a charger attached to a generator. That was good for only 12 volts. Now that I converted to 24 volt I need to purchase another charger I think. Can anyone suggest a good solution? I have 10 12 volt batteries wired to make 5 24 volt batteries all are rated the same 1000 / 200 hrs.
Tagged:
Comments
-
Hello Dailypix,
The Iota brand Chargers are popular for this use:
https://www.solar-electric.com/catalogsearch/result/index/?p=1&q=iota+chargerScroll down. There are many to choose from.
If your batteries are 100 Ah each, your battery Capacity could be about 500 Ah, in a perfect world. 10 percent of 20 Hour Capacity is the common charge rate target.
With parallel strings, equal current between individual strings of batteries is not certain, so some strings may draw more current that other strings ...
Many of the Iota chargers have a high AC Inrush current, which can cause issues with smaller gensets.
Just to try to get the discussion going.
FWIW, Vic
Off Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes. 25 KVA Polyphase Kubota diesel, Honda Eu6500isa, Eu3000is-es, Eu2000, Eu1000 gensets. Thanks Wind-Sun for this great Forum. -
Iota has been a good basic charger--Except that it had very high input surge current and a relatively poor power factor. Would require a larger genset to reliably run the Iotas. There is a new version of Iota with a "power factor corrected" input--I don't know anything about them otherwise--But should be worth a look (just checked, only available in 12 volt output--Never mind).
https://www.solar-electric.com/residential/batteries-battery-storage/battery-chargers.html
Another product that had some happy folks here was the Xantrex TC2 chargers. But they were very hard to get for a long time (our host even dropped them because of this--As recall from years ago).
http://www.xantrex.com/power-products/battery-chargers/truecharge-2-24v.aspx
What are your batteries (1000/200???)? Is each 12 volt battery rated 200 Amp*Hours (at 20 Hour Rate)?
The recommended rate of charge is 5% to 13% (for solar panels) and 5% to 20-25% for genset/AC utility chargers--Although, it is easier to overheat batteries with >13% rate of charge--So I would suggest that you monitor temperatures and have limited charging times (such as with a genset) when >13% rate of charge.
5% rate of charge is pretty low--And I would suggest 10% or so as a good compromise. If, you have 5 parallel strings of 12 volt @ 200 AH batteries, that would be a 24 volt @ 1,000 AH battery bank. That is a large bank and you would be looking at a ~100 Amp*Hour battery charger. There are not a lot of "generator friendly" 100 Amp 24 volt chargers out there--The inverter-chargers from major off grid system manufacturers do look like a good option (100 Amp charger is not rare)--And they are pretty programmable (charging set points, maximum AC input current control, etc.). I am not a fan of dual use devices (such as combined AC Inverter+AC battery charger)--But given the few large genset friendly battery chargers and some of the neat features of integrated AC inverter-chargers--They are difficult to ignore.
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Thank you for your comments. I believe one of my problems (among many as I got into this process knowing nothing and paying for my mistakes) is that I have too many batteries for my solar panels to support. I will begin by removing about half of the batteries because I am not getting a full charge with the solar panels even after several days without load except for a small energy efficient fridge.
By removing the batteries I should be able to top up the remainder with the solar panels alone.
It would be easier for the generator to charge the smaller bank in case of a heavy week of snow or two weeks of clouds.
I could charge up the disconnected batteries and give them four hours of trickle charging once in awhile when I have the generator on to run power equipment or the space heater when I first get up to the cabin in winter. Then if I have to I can swap out the depleted batteries for the spares. -
A "small efficient fridge" is, in fact, a pretty heavy load, and will suck batteries down pretty quick.
You may, if the chargers are transformer isolated, be able to use a pair of 12v chargers, one on each battery, but don't let
any wires touch, There is a chance the batteries can short through the chargers AC power cord so be careful,
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister ,
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 190 Solar Information links & sources, event announcements
- 886 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed