Fronius error code State 241
mbufton
Registered Users Posts: 1 ✭
Nice list of error codes:
http://gold-coast-solar-power-solutions.com.au/posts/fronius-primo-inverter-state-codes/
No "2xx" error codes at all????
Here is another document with "some" 2xx codes (not 241):
http://www.thesunworks.com.au/content/12_volt/Fronius_STATE_codes.pdf
From one website--It is possible that 2xx error codes are associated with Grid Voltage/Frequency/Other issues... I would check the voltage (and frequency) at the GT inverter's AC input. And inspect (and tighten with a screw driver) all AC connections from inverter back to the Branch circuit/breaker connections.
-Bill "my guess" B.
The state 241 code began coming up in many Fronius inverters this year. It is related to "arc fault" protection.
The older IG series requires AFCI card change to newest version. (changed out 12 in the last 6 mo)
The Primo series requires software update by USB.
As of July all new Primo inverters come updated. Anything before that needs the update.
Fronius will not provide me an answer as to the exact cause or why it has recently become a problem in Az.
Mark
Field Service Tech
Solarone Energy Group
Cottonwood, Az
Thank you Mark for the information.
I am posting here so as to maybe save those build systems from having any involvement with Fronius, I have 2 IG5100 that are 5 years old. One failed 6 months ago and the other one failed a month ago. I cannot get them to honor their 10 year warranty. There is no dealer with an hour and that one will not service the Fronius in-warranty unit. Fronius treats the end user with animosity. My second system has two Sunny Boy -- go SMA, avoid Fronius at all costs.hybrid: two xw6848 pro with four mppt60, 12 kw pv
17 cell 280ah LiFePO4 storage 14 kw (now at 3 banks) total 40 kw
gridtie: sunny boy sma 2x 5k
gridtie: fronius ag5100 two 5k (only one with 1.5k left) running on fumes
Gateway / Insight Local