Can someone give me a simple diagram in autocad on how to setup a 3pole / 3phase connection?

Chan
Registered Users Posts: 45 ✭✭
Can someone give me a simple diagram in autocad on how to setup a 3pole / 3phase connection? Do I need multiple inverter since normal inverter has a 2 pole input and output only or is there an inverter that is already a 3 phase connection?
Comments
-
How much power are you needing ? If just a little bit of 3ph, a single phase inverter into a 3 phase transformer could do the job. At some point, 3 inverters cost less than a big transformer
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Are you trying to do Grid Tied to a 3 phase utility power system--Then you connect 1-3x single phase inverters to your three phases based on voltage (i.e., if you are 220 phase to phase, then p1 and p2 to first inverter, p2 and p3 to second inverter, and p3 to p1 for third inverter--In the US, typical 10 kWatt maximum per inverter if less then 3 inverters). Also, in some cases, the utility may require something to turn off all 2-3 inverters if a single phase is lost.
There are two types of three phase power connections... Delta and Wye ("Y" or "Star"). Each type has different voltages (in the US, Wye is common for small business--120 from neutral (center of "star") to each hot leg, and 208 between each hot leg).
From what I have seen, most all smaller GT inverters are native single phase--Some have control inputs to detect/shut down on loss of phase. Only large inverters (50 or 100 kW and above) seem to have three phase native units.
If you are looking for off grid 3 phase power--That is difficult to justify three relatively large OG inverters (say 4-8 kW each) wired up to support three phase off grid (battery backed) power. These are very large systems (for off grid use) and not usually cost effective for smaller installations--And large installations are expensive (batteries, solar panels, inverters, wiring, backup genset, etc.).
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2.1K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 652 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 612 Discussion Forums/Café
- 305 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed