morning star ts60 mppt

renaultscenic2
renaultscenic2 Registered Users Posts: 16 ✭✭
I have the tristar ts60 displaying alarm and mppt,dont know why,can anyone help me out

Comments

  • BB.
    BB. Super Moderators, Administrators Posts: 33,431 admin
    edited June 2016 #2
    We can try--What type of alarm are you getting? What is your system configuration (solar array size, series/parallel connected panels, battery bank voltage and Amp*Hour rating)? How are you using the system (emergency backup, daily cycling, etc.)? How is the battery bank (voltage, specific gravity, state of charge)?

    If your batteries are discharged (below ~75% state of charge)--You need to get them recharged soon. Lead Acid batteries do not like to sit when discharged (and do not like deep discharging either).

    Unfortunately, there is usually not very much that can be repaired in the field for the electronics. We did have one controller where the two-color LED fell out during shipment and it was put in "backwards"-- And green became red (controller was fine, just the LED colors where reversed).

    I should also add--Check wiring and wiring connections. Loose/corroded/broken connections can cause faults too.

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • renaultscenic2
    renaultscenic2 Registered Users Posts: 16 ✭✭
    Ok thanks for the reply,i have 2 200watts panel with 2 200ah battery both the panels n batteries are in paralell,to power my house,everything works ok except the charge controller flashing alarm n mppt I have to remove the battery terminal to make it disappear but re-appears after some hours or days.
  • mike95490
    mike95490 Solar Expert Posts: 9,583 ✭✭✭✭✭
    If you can hook a computer to the controller and look at the LOG page, there is a row at the bottom labeled ALARM

    If you look at my example screen capture (attached) at day -10, you can see 2 events listed, and 1 is an alarm.   Linger your mouse over the red number in the live webpage, and you get a pop-up at the cursor of the name of the alarm.  (mine on day -10 was a controller reboot)  All the days with 1 event, is Float.

    Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister ,

  • renaultscenic2
    renaultscenic2 Registered Users Posts: 16 ✭✭
    I think mine is alarm 21

  • BB.
    BB. Super Moderators, Administrators Posts: 33,431 admin
    edited June 2016 #6
    If your alarm is at 21 volts (Battery Bus Voltage--And not MorningStar's alarm code #21)--Then your batteries are "dead" (or near dead). In general, older lead acid batteries that have been taken "dead" will fail in days to a couple of weeks (new is less than one year old, older is 3 years and older). The longer a battery bank sits (uncycled) below ~75% state of charge, the faster the bank will sulfate (and eventually, die).

    Note: a 24 volt lead acid bank should not be taken below ~50% state of charge very often (longer cycle life) and never below ~20% state of charge (various reasons). Lead Acid battery bank voltages are not very accurate for estimating state of charge--But, roughly, (at room temperature) avoid taking your resting voltage much below ~24.0 volts (hours of 'resting'), and your under load voltage much below ~23.0 Volts (under normal loads--High surge current could take a partially discharged bank down to 21.0 volts for a few seconds).

    So--Next question, why did the bank go to 21 volts? Was it too much load current*hours of discharge? Bad Weather? Too small of solar array/amount of sun for your loads? Failed solar panels/bad wiring connections/failed solar charge controller/failed battery bank?

    At the very least, try to get your battery bank charged quickly (genset, utility power on AC battery charger). At a minimum of 5% to 10% (better) rate of charge. The longer they sit at "dead", the less likely you will be "lucky" to bring back your bank.

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • renaultscenic2
    renaultscenic2 Registered Users Posts: 16 ✭✭
    Everthing is ok now after disconnecting and reconnecting the cc.
  • BB.
    BB. Super Moderators, Administrators Posts: 33,431 admin
    Hmmm...

    For most charge controllers, connect the battery bank first and the solar panels second.

    If you do the opposite, it can confuse the charge controller.

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • South Africa
    South Africa Solar Expert Posts: 295 ✭✭✭
    edited June 2016 #9
    Jip, I did that once, panels first then batteries, because I swapped the batteries. Controller thought for a week it was a 24v bank, instead of a 12v one. had to reset the controller using a PC and controller serial cable.

    At least the old batts got a good equalise, a VERY good one.  :D
    5kVA Victron Multiplus II, 5.2kW array, 14kWh DIYLifepo4 bank, all grid-tied.